Evening all
Anyone any ideas on a voltage being present on pipework in a flat?
All bonding done and satisfactory Ze at board.
It’s a block of 3 which I’ve isolated all Power to two of the flats the third is a holiday home which I can’t access. I was thinking there is an issue either in the inaccessible flat or an external problem. Any ideas would be appreciated. The incomer to the two I can access is a tn-s 3 phase.
Cheers
 
possible fault current flowing to earth through the pipe?. could be that the fault current is not sufficient to trip any protective device fitted?
If the pipe runs through the building then the fault could as you said be in any of the flats??
Are you able to access the cutouts for other flats? came across a similar on a TT once where the rod was disconnected as somebody stole the cable! and system was using water pipe as the main earth.
have you fully checked all the bonding and that the necessary clamps are all secured properly?
 
Last edited:
If Ze and bonding are ok then there can't be much voltage on the pipes, surely? Need a lot of current to generate a potential across 10m of 10mm (say) and that should trip any RCD and probably the circuit breakers too?
 
I have had a siuation where after investigation, 0.74 volts was coming in to an installation from outside and finding its round the earhting to return to the substation.
 
Was measuring 48 volts using mft. I have measured ze at cut out in flat. The cut out in flat is tapped off the 3 phase tns at entrance stairwell to two of the flats. Im heading back tomorrow to make sure I’ve not missed anything stupid, cheers for replies so far.
 
I would suggest you check the Ze at the DNO head with all paths removed.

I had this once and it was a dodgy TN-S and a R1+R2 link left in on another flat.

The funny thing is because I reported the poor Ze to the DNO when they put a PME link and everything was sorted I thought no more of it.

It was two years later when I went to test a different flat and spotted the R1+R2 link left in that I put 2 and 2 together. Clearly when the DNO sorted their earth out it tripped the MCB in the flat with the fault as it should have.
 
pull the breakers one by one, see which circuit is using the ground as a neutral return path.
Bear in mind that it may not be your installation causing this,
it could be the neighbors installation.
 
It is looking like a neighbouring property that is a holiday home so this could drag on. The dno isolated as many properties as possible and the fault was still there. Dno engineer said he would phone me back which will probably be tomorrow.
 
Evening,
I have just found a problem that I had with taps giving us a little buzz every now and then, but not enough to trip the RCD's in the CU. I found we had an intermittent 22v coming through the main earth on a TN-S system. I found the 22v by checking the bonding and then measuring between the MET and the main earth. To cut a long story short, it was a fault in the street lights outside that was sending voltage to the earth at the transformer down the road.
 
Evening,
I have just found a problem that I had with taps giving us a little buzz every now and then, but not enough to trip the RCD's in the CU. I found we had an intermittent 22v coming through the main earth on a TN-S system. I found the 22v by checking the bonding and then measuring between the MET and the main earth. To cut a long story short, it was a fault in the street lights outside that was sending voltage to the earth at the transformer down the road.
Earth fault voltage from outside the installation will not trip RCDs inside the installation.
 
Did hear a story a few years ago about the gas engineers that go a shock when cutting a gas pipe as the home owner bypassed the meter and stuck the neural able to the gas pipe, may be an "Urban Myth"
 

Reply to Live pipework problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
945
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
715
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
601
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
828
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock