Several vectors have been generated by my original innocent question of whether the maximum current load on a domestic circuit, in relation to the maximum amperage limit (or 80% of that) of the supply, should be calculated on from the peak use in kW (dividing Watts by the supply voltage), or, if there is reason to consider the particular installation to have a power factor of less than 1, in kVA (finding the higher amount of Amps from this in the same way).While you are concentrating on the heating output and trying to achieve something similar to what you have now in the future you have to bear in mind a lot of the newer technologies rely on an increased level of property insulation to deliver the most effective results
I was always a bit sceptical of the passivhaus building methods until I got involved in a project that a local vet was building, he is very into the eco concept and built a new surgery to passivhaus spec with heat recovery, ASHP, solar panels and masses of insulation, the end result is very effective and costs very little to run but it does involve more cost. One of this guy's other projects was renovating his own house Low Energy Building Consultancy | Kingsleypassivhaus | Frodsham - https://www.kingsleypassivehouse.com/ it might seem a bit extreme but with the ever rising energy costs it has to be an option
I still don't have an answer to that question, but I have had several "non-answers" which are very interesting.
Your intervention is among these vectors.
We don't want to rebuild, or move, but we do accept that the already well-above-average performance of our 1968 house could be further improved. You imply that this should not necessarily be done only if clearly cost-effective over a reasonable term. We are prepared to look at this, although we do not see at present how this house could be made substantially more suitable for our needs, even with major disruption.
But we will look at the website whose address you have provided. Many thanks!
RE YOUR FIRST WORDS ABOVE
My original question to members of this website arose from the task I had set myself of trying realistically to assess how many extra Amps could be absorbed safely by our existing single-phase 23 kVA mains circuit.
That was with the view of trying to establish:-
What extra electrical load would be involved by replacing by electrical appliances our gas boiler, a gas convector heater in our lean-to utility room (this heater may no longer be strictly necessary due to substantial improvements to the insulation of that room post-dating the addition of the heater in 1997), and our venerable but brilliant Cannon gas cooker (with fold-way high level grille/rotisserie: 5.275 kW, but that will be the energy input figure).
Additionally I would need to take into account that an electric c.h. boiler, replicating the 22 kW output of our gas boiler, would need 3-phase current. This, according to our DNO, would reduce the kVA of the single-phase input from 23 to 18.4. Not good news!
I know our typical annual gas consumption over enough years to have a realistic estimate of it for one year.
With the well authenticated figure of 76% for the output of our gas boiler in relation to its 28 kW input, I used, as you noticed, the same rating (22 kW to be on the safe side) for a proposed electric boiler.
I have now been struck by how much greater is the annual requirement for kVA if we went "all-electric" than it shows when adding our current consumptions (in kVA for present single-phase installation to our gas consumption.
I estimated consumptions for the three appliances which would be replaced, and added these to our current single-phase consumption in kVA. I calculated the consumptions of the replacement electric appliances, with use periods and levels of power drawn to match what I estimate applies now to our mixed installation.
The total known annual consumption of gas as useful energy is around 20,000 kWh.
But I found it impossible to arrive at a figure as low as 20,000 kWh/pa for the present boiler alone with what seems to be its work pattern Modifying this pattern to produce a suitable figure (well below 20,000 because I have to include figures for the heater and cooker) have made it pretty clear that the present boiler is too powerful for our 2019-21 needs, even if was only slightly OTT when specified and fitted in 1997.
In fact, it looks as if we need only about a 15 kW boiler, or even less. Interestingly, our local service man spontaneously declared last year, when he serviced the boiler, and changed the gas valve (the only major component that this boiler has ever needed - apart from flue fans, which I can fit legally myself, that 15 kW was "quite enough for a house of this size and kind".
So we'll try to find someone qualified in energy assessment to produce a heat requirement for our home before I do much more work on my forecast.