Discuss Load on non RCD side, causes RCD trip in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi

Looking for advice on a intermittent fault. New dishwasher is causing RCD to trip (happened with two new dishwashers - supplier changed it for me). Thinking therefore it was an issue with the ring main, I plugged it into the cooker socket but it still trips at some point during the dishwasher cycle. This is the dedicated one for the cooker and not protected by the RCD (i.e. split RCD consumer unit).

Could the load from the dishwasher, exaserperate a problem with one of the RCD protected circuits (maybe split neutrals)?

Thanks in advanced for pointers.
 
Search for an apparently unrelated N to E fault.
Could be on any circuit.
[automerge]1588456640[/automerge]
Whilst your at it, have a look at other posts.
There are plenty of similar threads on here.
 
Last edited:
The N-E fault will invariably be on a circuit protected by the RCD that trips, even if the load (dishwasher) that provokes the trip is not. The fault can also be within an appliance connected to a protected circuit.
 
Thanks - that helps narrow where I look and started to turn-off to eliminate :)
what you need to do is to switch off each breaker in turn, also disconnecting the N. start with the circuits not on the RCD that trips. with 1 circuit disconnected in CU, turn on the heavy load (dishwasher appears to trip when on a heat cycle) and find out which circuit, when disconnected, cures the fault. that's where your N-E fault will be. last one i had was the shower had the N-E fault in the pull switch.any decent size load on the other RCD caused it to trip.
 

Reply to Load on non RCD side, causes RCD trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
614
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
827
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock