Search the forum,

Discuss Loop into Fan in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi all new to the forum


Learning the trade as an improver, trying to get my head round something.

When taking a feed from the light switch to the fan.

Normally I would P live in Com and SL in L1

So had to attach a three core then up to fan, so does permanent stay in Com or go down to L1 has anyone got a simple scenario. I just can’t see atm
 
Welcome to the forum.
Simple scenario 1, traditional ceiling rose wiring with just PL and SL at switch:
1715033653171.png


Scenario 2 - Loop in and loop out at the switch with N and PL at the switch:

1715033864449.png



In both cases:
Grey is sleeved blue, and takes N to the fan via isolator (see below)
Brown takes PL to the fan via isolator.
Black takes switched live to the fan via isolator.

The 3 pole isolator simply interrupts all of them to allow maintenance of the fan..
CPC omitted from diagrams

Does that help?
 
Hi all new to the forum


Learning the trade as an improver, trying to get my head round something.

When taking a feed from the light switch to the fan.

Normally I would P live in Com and SL in L1

So had to attach a three core then up to fan, so does permanent stay in Com or go down to L1 has anyone got a simple scenario. I just can’t see atm
Hi Mate you would also require a Neutral and by default a cpc.
Is the relevant light fitting wired as a 3 plate (loop) system? If so you will have all the connections you need for a fan, including a timer version.
If not you will have to source a neutral from the same circuit and through a 3 pole isolator.
 
Where is the loop connection? No good taking a 3 core to the switch if is wired in 3 plate at the ceiling rose.

Welcome to the forum.
Simple scenario 1, traditional ceiling rose wiring with just PL and SL at switch:
View attachment 116290

Scenario 2 - Loop in and loop out at the switch with N and PL at the switch:

View attachment 116291


In both cases:
Grey is sleeved blue, and takes N to the fan via isolator (see below)
Brown takes PL to the fan via isolator.
Black takes switched live to the fan via isolator.

The 3 pole isolator simply interrupts all of them to allow maintenance of the fan..
CPC omitted from diagrams

Does that help?
 
Thankyou all for reply’s! Wiring
G diagrams are brilliant.

From a 3 plate pendant I get that no issues.

It’s more when taking from the switch PL still stays in the common? Let’s say converting a normal bathroom light. Which has PL in common neutrals in block. SL in L1.

Do these cables stay where they are, before introducing the 3 core. I get the isolator part that’s find
 
An alternative to the triple pole isolator is to fit a switched FCU into the supply to the bathroom light circuit. This provides the necessary isolation and the often specified 3A fuse.
Downside is that the fan can't be isolated and the light remain on, or, alternatively, the upside is that the occupants can't use the shower without the fan running and cover the walls in mould.
 
I have posted this years ago, it is the way I wire fans which gives the fusing required by a lot of manufacturers and the isolation required allowing the light to operate when the fan is isolated, a lot more convenient at night if you only want the light on.
Really only for new work or very straightfoward to do if there is an easy route from switch to existing isolator. It looks busy but the only difference between this and what is usually done is that instead of running a 3c from switch to isolator you run 2 x 2c, one is taking the supply l & N, the other is a switch wire for the now fused L to and from the switch
 

Attachments

  • fan wiring.jpg
    415.7 KB · Views: 19

Reply to Loop into Fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Part 1. I Have 2 red wires and one brown going into my ceiling pull chord UK light switch in bathroom. BROWN AND RED into L1 and RED into COM...
Replies
1
Views
1K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
955
Sorry for the long first post, I wanted to be as thorough as possible. On my landing I have a 2-way switch setup, one of which is 3-gang, one of...
Replies
5
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock