Lounge lights not working.
No RCD tripping.
No MCB tripping.
Lights wired power-switch-light. New switch and pendant installed.
Meggar test shows following voltages when switch is off.
L-N 235V
L-E 235V
N-E 18V

When light is switched on,
L-N 235V
L-E 235V
N-E 175V

Is someone able to give some advice as to why I may be getting these readings. Continuity and polarity tests fine.
Lights still not working.
Thanks in advance.
 
Dont think the OP is a Spark HS

Not sure I agree with that, the op states continuity and polarity good

Edit : having read a couple of previous threads I don’t think he is, nor does he appreciate and questions about ability .......he just expects answers on a plate
 
Last edited by a moderator:
Not sure I agree with that, the op states continuity and polarity good

Edit : having read a couple of previous threads I don’t think he is, nor does he appreciate and questions about ability .......he just expects answers on a plate
Glad you agree with me.
 
Meggar test shows following voltages when switch is off.
L-N 235V
L-E 235V
N-E 18V

When light is switched on,
L-N 235V
L-E 235V
N-E 175V

‘Megger test’ is the common term for an insulation resistance test, but your test results imply that you’ve measured the voltage. Can you clarify what you mean here?
 
Have the lights stopped working after the new switch and pendant were installed? Or were these installed due to the fault, in the hope they might fix it?
 
more info is needed here, what location are you testing from?
what is the total length of the circuit from the ring or radial to the lamp?
the original post lends a lot of questions on the qualifications hence the reason for asking if the OP is a spark
 
He can't be a spark as he'd know that with the switch off, L-N would be 0V not 235V.

With the switch on N-E is giving 175V. I've had similar in the past where the N was an unsleeved L and the client in replacing the pendant had got everything mixed up so when the switch was on the switched L was going through this light and the next light in series.

He needs a professional with test gear and more importantly knowledge to get it sorted out safely.
 

Reply to Lounge light neutral problem in the Lighting Forum area at ElectriciansForums.net

Similar Threads

M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
319
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
483
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
747
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
402
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock