Discuss low ac volt reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

ambrad

After installing a garage unit i carried out a voltage test at the furthest point of the installation. i got a reading of 112.5 v L-N. I checked it L-E and got 242v.

I ended up back at the rcd and measured the live side and got 242v. When i checked the load side i got 112.5 v. I disconnected the load live from the breaker and got 1125v again. Does this indicate a faulty rcd or could there be some other issue i am missing. Just to let you know the load was only an ac isolater ready for a solar pv system.

Help please.

thanks
 
sounds like a faulty RCD, on the neutral side. just make sure the connections on the RCD and N bars ar good and tight.
 
Sounds like the neutral may be missing, take the tests again with an analogue tester you'll probably see the fault a lot more clearly.
 
Yep, an analogue voltmeter can be worth their weight in gold at times!! lol!! A must have for every electrician, even if it's a cheapish bog basic model.... Just don't throw it about too much!!
 

Reply to low ac volt reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
628
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock