Hey people,

I did some testing for a sporadic RCD trip this week.

The customer did some playing about and narrowed it down to the garage.

Tested the garage circuits and all were good. Tested the feed and found with the CPC still in the bar I got 0.076 meg but when I pulled it out the fault cleared.

All I can think is it's chaffed through somewhere like maybe on a CH pipe? but just thought I would check I'm not doing something stupid before pulling in a new feed.

Cheers,

Luke.
 
It going high with the CPC off the MET implies the fault is L to true earth, not the cable's CPC

So most likely insulation damage as you say but 0.078M is too high for a direct metal-metal contact to Earth, but an otherwise floating metal water pipe (i.e. electrically isolated from whole system by plastic sections), a charred cable (or fried rat remains), or a water filled accessory might explain it.
 
Thanks for the help PC, I went back today and found it.

The feed comes out the house into a junction box, under the path in SWA and into another junction box. When I looked in them last week everything looked good and earthed with a banjo at one end and the IR was high on that section.

I disconnected both ends today and check IR with a wander lead back to the MET and low and behold there was the fault, pulled the dust cover down and the SWA had been pulled out the gland on the banjo end ? Customer said she had the patio done a couple of years ago and he was in and out down the alley on a mini digger for days where the SWA was.

Thanks again for the help.
 

Reply to Low IR reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
688
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
412
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
667
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock