Hate these. Been called out to troubleshoot a tripping MCB. It's a house I've been to before and I know the wiring is a real dogs diner, but anyway.

Got an MCB that's tripping out with no appliances plugged in. The sockets themselves are not in a great state, however continuity and insulation resistance tests across the circuit showed no problems (Did that at every socket on the radial). Turned on the breaker and within 5 minutes or so it tripped out. Not seeing any singeing on the conductors or sockets.

Now I have to say, last year I attended this house and replaced a burnt out MCB (Different circuit) - surely this couldn't be a second one. The board is only maybe 10 or so years old (Hager).

In my experience these rarely turn out to be cable faults as it would show up in the insulation resistance test, so I'm left with one or more dodgy sockets (6 total on this radial), loose wiring or a broken MCB.

Any other thoughts ?
 
Ok, little bit further forward. I've narrowed it down a bit now. I thought I had a ring with a spur, but it turns out I have 3 independent radials all in one MCB, which is ok, messy, but not against the regs. So, I've isolated the faulty radial now which has 3 sockets on it, 2 in hall way and 1 in the lounge. At least it's got their kitchen and combi boiler up and going - so I just need to find out what's wrong with that radial. The sockets are in an awful state, so I might just clean up the conductors and back boxes and replace the socket fronts. I redid the continuity and resistance on that circuit and they came back fine (0.4 at furthest point, 0.3 nearest the board and >2000Mohms on the IR) - Perhaps you could argue the resistance values might be a little high for a radial that's perhaps 10m long but it's definitely not a cable fault, and it's not an MCB issue either now as everything else is fine. As an aside I found the boiler hadn't been earthed! So sorted that out.
 
Assuming it's a correctly functioning B16 breaker, a trip after 5 minutes (300 seconds) suggests roughly 28A of current.
With equipment connected, it might be worth trying a L-N continuity test on that branch and see if you happen to get about 8-10 ohms. Worth a shot! It's unlikely there will be a purely permanent resistive load but it doesn't take long to try.

It could be a faulty socket / plugged in equipment on that branch.
It could also be that something hungry on that branch is simply bringing the total draw up considerably and the whole circuit is overloaded.

The earlier suggestion of a clamp meter is really the way to go.
It sounds like you are getting there!
 
Thought I'd found the issue. Found one socket with loose line and neutral conductors, so got those sorted, then I found a socket that was rusty, so sorted that, powered up and nothing tripped out....until a few minutes ago when I got a call. So the tripping has gone out from once every few minutes to once every couple of hours. Client has discovered a socket hidden behind a cupboard that they never knew was there, so going back to have a look.
 
Thought I'd found the issue. Found one socket with loose line and neutral conductors, so got those sorted, then I found a socket that was rusty, so sorted that, powered up and nothing tripped out....until a few minutes ago when I got a call. So the tripping has gone out from once every few minutes to once every couple of hours. Client has discovered a socket hidden behind a cupboard that they never knew was there, so going back to have a look.

Have you measured the current flowing through the circuit yet?

How do you think the loose connection or rusty socket could have been causing the MCB to trip?
 
If you don't have one, a very basic AC clamp meter can be had for £30 at screwfix and would be of immense help with this fault.
No point chasing your tail if it's simply too many things on the same circuit!
So, I've isolated the faulty radial now
At the moment I've read nothing to conclusively prove that this branch is faulty. Are you sure it's faulty?
If you connect this branch again and can reliably get trips every 5 minutes, you could try swapping each socket for 3 wagos.

If there's a fridge freezer (with defrost element that periodically operates) or anything with a timer and a heating element plugged in I'd also be suspecting that, and a bit of PAT testing might help.
 

Reply to Maddening MCB Tripping fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock