Ok, little bit further forward. I've narrowed it down a bit now. I thought I had a ring with a spur, but it turns out I have 3 independent radials all in one MCB, which is ok, messy, but not against the regs. So, I've isolated the faulty radial now which has 3 sockets on it, 2 in hall way and 1 in the lounge. At least it's got their kitchen and combi boiler up and going - so I just need to find out what's wrong with that radial. The sockets are in an awful state, so I might just clean up the conductors and back boxes and replace the socket fronts. I redid the continuity and resistance on that circuit and they came back fine (0.4 at furthest point, 0.3 nearest the board and >2000Mohms on the IR) - Perhaps you could argue the resistance values might be a little high for a radial that's perhaps 10m long but it's definitely not a cable fault, and it's not an MCB issue either now as everything else is fine. As an aside I found the boiler hadn't been earthed! So sorted that out.