Currently reading:
Magnetic lock timer not working.

Discuss Magnetic lock timer not working. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Tried fitting a magnetic lock on a job for a bathroom. Client has had problems with people doing drugs in his bathroom so wanted to control entry from his shop tills so the lock is fitted and works but I need it to be sorta timed as when releasing, the button locks the door( staff can't use the toilet without one of them holding the button for the other) I'll attach a diagram of what I've done can someone let me know what I've done wrong?

Badly drawn diagram: 1641480108519-615884853 - https://ibb.co/C7yb6Js

DB= distribution board
T= transformer pack
Ml=magnetic lock
Pbb =push button at tills
Pbd =push button inside bathroom

First time wiring up a mag lock and I have no diagram
 
Looking at the drawing, the wiring is wrong if this is a maglock that you have installed, the release buttons need to be in series in order to drop the power to the lock in order to release it.

The drawing shows the buttons in Parallel so this will cause a short circuit on the lock supply, so I cannot see how it works at all if it is wired to the drawing.

A timer is always the best option, I have used loads of these without a problem;

 
I think I may have done my diagram wrong to how I've wired it.

Here's the transformer with my feed coming in and a flex leading out to my first switch

Feed in
IMG_20220107_090859.jpg


Cable out to the switch
IMG_20220107_090938.jpg


First switch in the till station white labled as n.c
IMG_20220107_091054.jpg
next switch inside the bathroom
IMG_20220107_090751.jpg

Finally the mag lock itself
IMG_20220107_091123.jpg
 
Do you have the connection diagram for the transformer as it looks like your wiring is wrong
It looks like the door release buttons should be connected to terminal 6 and possibly terminal 5 as normally open buttons
With the magnet directly connected across terminals 1 & 2 when you press the release button you will get a timed lock release
 
Hi, I have come across one of those power supplies in the past, it has a built in timer to release the lock.

The lock is wired into terminal 1 +ve and Terminal 2 -ve

The release buttons are normally open so you use the green pair on each one, wired in parallel. These are wired into terminals 5&6 it doesn't matter which way round.

The lock release timer is adjusted by the pot to suit the site as required.
 

Reply to Magnetic lock timer not working. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock