Just some clarification please.
Max demand for cooking devices.
OSG says 10A + 30% of "connected cooking appliances in excess of 10A + 5A" if a socket is available in the isolator. The oven and hob are two devices. Does the 15A apply to both of them or just the first one?
eg: Oven 4.8 kW Hob 5.5 kW. With a socket available.
15A + (((0.3 x 4.8) + (0.3 x 5.5))/230) = 28.4A
or
15A + ((0.3 x 4.8)/230) + 15A + ((0.3 x 5.5)/230) = 43.43A
Thanks in advance