Just some clarification please.

Max demand for cooking devices.

OSG says 10A + 30% of "connected cooking appliances in excess of 10A + 5A" if a socket is available in the isolator. The oven and hob are two devices. Does the 15A apply to both of them or just the first one?

eg: Oven 4.8 kW Hob 5.5 kW. With a socket available.

15A + (((0.3 x 4.8) + (0.3 x 5.5))/230) = 28.4A

or

15A + ((0.3 x 4.8)/230) + 15A + ((0.3 x 5.5)/230) = 43.43A

Thanks in advance
 
Just some clarification please.

Max demand for cooking devices.

OSG says 10A + 30% of "connected cooking appliances in excess of 10A + 5A" if a socket is available in the isolator. The oven and hob are two devices. Does the 15A apply to both of them or just the first one?

eg: Oven 4.8 kW Hob 5.5 kW. With a socket available.

15A + (((0.3 x 4.8) + (0.3 x 5.5))/230) = 28.4A

or

15A + ((0.3 x 4.8)/230) + 15A + ((0.3 x 5.5)/230) = 43.43A

Thanks in advance
Good question, not sure will ask around, Personally I would say the hob and the Oven are qne cooking device, some of the active members may be able o provide an answer.
 
First and foremost I'd refer to connection instructions for both appliances. I'd personally want a circuit for each of those appliances.
 
First and foremost I'd refer to connection instructions for both appliances. I'd personally want a circuit for each of those appliances.
So a seperate MCB for each? Not unreasonable but I have never seen it. Friend of mine has just had an old house completely rebuilt and rewired. Including new kitchen. Oven and hob are connected to the one B32. Treating them as one device only comes to 29A with 11kW full load.
[automerge]1594642457[/automerge]
Good question, not sure will ask around, Personally I would say the hob and the Oven are qne cooking device, some of the active members may be able o provide an answer.
Treating them as one device only comes to 29A with 11kW full load. So that woud be fine.
 
So a seperate MCB for each? Not unreasonable but I have never seen it. Friend of mine has just had an old house completely rebuilt and rewired. Including new kitchen. Oven and hob are connected to the one B32. Treating them as one device only comes to 29A with 11kW full load.
[automerge]1594642457[/automerge]

Treating them as one device only comes to 29A with 11kW full load. So that woud be fine.

Yes I always try and divide the installation as much as possible. I have been known to add 6 new circuits on a kitchen fit.
It may be fine diversity wise. You can get a double outlet plate if doing this. The manufacturer's instructions for each appliance may say to connect to a dedicated 32A circuit though so worth checking them out and taking that into account in your design.
 
Yes I always try and divide the installation as much as possible. I have been known to add 6 new circuits on a kitchen fit.
It may be fine diversity wise. You can get a double outlet plate if doing this. The manufacturer's instructions for each appliance may say to connect to a dedicated 32A circuit though so worth checking them out and taking that into account in your design.
A totally get that to be honest. When I first encountered the diversity rules I found the probability aspect of the diversity calcs a little uncomfortable but I understand why it's done that way. It takes into account the intermittent nature of thermostatic controls. It keeps the costs down and costs are important at the end of the day. I know of one socket circuit in a commercial kitchen that has 16 13 amp outlets on a B32.
 
I would add together the ratings of all cooking appliances on the circuit, and apply diversity to that. It's exactly the same as if it was just one combined oven and hob. The example you give would go comfortably on one circuit.

There's a good JW youtube on this:
To view this content we will need your consent to set third party cookies.
For more detailed information, see our cookies page.
View: https://www.youtube.com/watch?v=QQduU8RkjD8
 
I would add together the ratings of all cooking appliances on the circuit, and apply diversity to that. It's exactly the same as if it was just one combined oven and hob. The example you give would go comfortably on one circuit.

There's a good JW youtube on this:
To view this content we will need your consent to set third party cookies.
For more detailed information, see our cookies page.
View: https://www.youtube.com/watch?v=QQduU8RkjD8
That would be 28.43A. Thanks.
 
I would be happy to have both appliances on one MCB (32A) with one isolation switch (as long as both oven and hob are close enough to each other to maintain local isolation) and a dual cooker outlet plate.

As for diversity, I would treat them separately. It doesn't make sense to me to treat them as one item as they are not. If one item is on full there is no limiting device to make sure the other is not. However, if there is only one isolation switch with a socket outlet then the additional 5A (with regards diversity) is only added once.

Oven = 4.8kW = 21A.
Diversity = 10A + (0.3x11A) = 13.3A

Hob
= 5.5kW = 24A.
Diversity = 10A + (0.3 x 14A) = 14.2A

max demand = 13.3A + 14.2A + 5A(socket) = 32.5A

I realise the max demand is 0.5A over the 32A MCB but as I have rounded up the initial current for both appliances I would say it's OK. You could fit a 40A MCB assuming using 6mm cable and acceptable reference method.
 
Last edited:
as above comments. up to 15kW cooking appliance on a 32A circuit is fine has been for donkeys years. wrt Andy78's post, putting them on separate circuits is a good idea though, purely for the fact that if 1 appliance has a fault and needs to be isolated, the other one will still be usable. depending on which one can still be used, you have a choice of oven chips or chip pan chips.
 

Reply to Max demand for double oven and hob in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top