Discuss Max Earth Fault Loop Impedance for OverCurrent Devices Before Amendment 3 and Now??? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
95
Maximum Earth Fault Loop Impedance for OverCurrent Device was calculated
230/(MCB Rating*5) * Rule of Thumb
is that correct?

And how are they worked out now after Amendment 3?
 
Last edited:
same as before but with a 5% reduction to allow for dupply voltage low limit of about 216V. think it's called a Ci factor.
 
Thanks ill try it but I just read on another forum
"The IET don't actually calculate it - it derives from the circuit breaker product standard."

------.org/forums/forum/messageview.cfm?catid=205&threadid=39081

don't know if it's garbage?

[automerge]1583529462[/automerge]
Sorry it works perfectly, Thanks again.
 
Last edited:
Thanks ill try it but I just read on another forum
"The IET don't actually calculate it - it derives from the circuit breaker product standard."

------.org/forums/forum/messageview.cfm?catid=205&threadid=39081

don't know if it's garbage?

[automerge]1583529462[/automerge]
Sorry it works perfectly, Thanks again.
WTF is That???
 
thought i was going cross eyed and almost binned my Scotch.
 

Reply to Max Earth Fault Loop Impedance for OverCurrent Devices Before Amendment 3 and Now??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
527
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock