I'm just hoping I can cross reference my knowledge or be corrected by someone on a quick query. It's a test question I'm doing but I'm querying the answer I've been given.

I want to find the Max permitted Zs on a 3036 45A fuse. I was under the impression that I should reference table 41.2 in the regs for the max permitted Zs value if the circuit is a final circuit (rather than a distribution circuit), and the system is not a TT. The answer I've been given has sent me to table 41.4, for a 5 sec disconnection time rather than a 0.4 sec disconnection time. Is there any other reason why the answer may be sending me to the 5 sec disconnection time table rather than the 0.4 sec table (other than the two points I've mentioned above)?

Any help would as always be massively appreciated.

Thanks again.
 
At 45a it is usually fixed resistive loads and not socket circuits or lights at 32a and 6a among other values. Hence the 5s permissible time as I understand if that is what you are getting at?
 
Hi - looking at Fig 3A2(b) a 45A BS3036 fuse needs 390A to melt in 0.4 seconds, if that’s the disconnection time needed. So using 0.8(temp) x 230V x 0.95 (Cmin) / 390A, I got 0.45 Ohms as the max test value.

Edit - which of course isn’t your question really, but @haptism has it I reckon :) .
 
Last edited:

Reply to Max Permitted Zs for 3036 semi enclosed rewirable fuse... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock