How does max volt drop for 25mm or 35mm feeds to sub CU work.

Do we for example allow only 1% drop on the 25/35mm so we can keep 2% drop for lighting circuits and 4% for power circuits, or is there any where else in the regs that gives specific figures on maximum allowed volt drop? Any difference for single phase or 3 phase supplies?

Thanks.
 
Single phase is no different to three phase in terms of vd but you are on the right track. 2% is often an unwritten rule of thumb for submains but this is flexible depending on your vd for final circuits at the served distribution board.
 
Depending on the cable length trying to keep to 1% could be rather expensive! Ideally you would work through acceptable combinations of feeder size and final circuit sizing to see what is best overall value for money.

Three phase is more tolerant simply as you have a higher voltage (or are assuming cancellation of current on the neutral) but the same idea as westward10 said.
 

Reply to Max volt drop for 25mm or 35mm feed to sub CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
629
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
920
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
626

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock