Had a bit of a brain freeze. Got to go and do an inspection on a property with 2 consumer units, the 2nd fed from the first on a 50A MCB.

Let's say theoretically I get 0.2 for the Ze on the main board, then 0.3 for the Zdb at the second board and 0.2 for R1+R2 on a ring final on a 32A MCB.

Is my max Zs for this circuit 0.7 ? Max Zs = Ze + Zdb + (R1+R2)
 
The measured Zdb for the 2nd board incorporates the earth path of everything up to that point.
So the Max ZS for the ring final circuit on the 2nd board is the dead R1+R2 result added to the Zs at 2nd DB.

So in your example it would be 0.3 + 0.2 = 0.5
 
Last edited:
To add, that will include parallel paths if bonding is connected at 1st DB, so if you are wanting to calculate Zs for a circuit on the 2nd DB it would be more accurate to add:
Ze + [(R1+R2) of distribution circuit to 2nd db] + [(R1+R2) of final circuit]
 

Reply to Max Zs multiple boards in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top