Discuss Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net

Just for my sanity... Are you saying that if the Max Zs value for the respective circuit exceeds that of 80% we should instead input 1667 instead to allow for the Max value for a 0.03mA RCD? In the Max Zs field?

On an EICR I would yes.

I would not on an EIC unless it was designed to be.
 
Hummm. Horses and courses n all that. I'd complete the field as required and complete the 30mA section so the certificate detailed the correct OCPD and associated Max Zs and/or RCD type.

Can anyone shed any light on this? Have they had this discussion with their area engineer?
I’m not sure why you would need the discussion with your area engineer? What value would you record on the schedule if it was TT....The max Zs value of the OCPD or the max Zs permitted for the RCD that’s providing the earth fault protection? It’s clear to me what you should be doing.
 
Hummm. Horses and courses n all that. I'd complete the field as required and complete the 30mA section so the certificate detailed the correct OCPD and associated Max Zs and/or RCD type.

Can anyone shed any light on this? Have they had this discussion with their area engineer?

I do not need to speak to my NICEIC Engineer. I understand what is required.

How else would you meet disconnection times if the Zs is too high?
 
Is there an excerpt from BS7671 that details this (Use of max RCD values) over the Max Zs of the OCPD when considering Zs values that exceed the 80% factor?
 
Is there an excerpt from BS7671 that details this (Use of max RCD values) over the Max Zs of the OCPD when considering Zs values that exceed the 80% factor?

To be honest the use of an RCD to cover fault protection on a TN system is not ‘textbook’. But sometimes you need to think outside the box. There are otherways to combat this issue, which is only an issue due yo poor design but it is completly unrealistic to rewire a circuit due to high measured Zs when an RCD will provide protection and still meet 7671.
 
To be honest the use of an RCD to cover fault protection on a TN system is not ‘textbook’. But sometimes you need to think outside the box. There are otherways to combat this issue, which is only an issue due yo poor design but it is completly unrealistic to rewire a circuit due to high measured Zs when an RCD will provide protection and still meet 7671.

Absolutely! Couldnt agree more. But is there an excerpt for stating one value over the other? Or is this just an understanding you have with your engineer. I'll definitely raise this with mine tomorrow if thats what you guys/girls are doing and its deemed acceptable.
 
Absolutely! Couldnt agree more. But is there an excerpt for stating one value over the other? Or is this just an understanding you have with your engineer. I'll definitely raise this with mine tomorrow if thats what you guys/girls are doing and its deemed acceptable.

I don’t run anything by my engineer.

You used the value of whatever the OCPD is that you are using.
 
What the foot note on the model form says is...

"Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in chapter 41 of this standard, state the source of the data in the appropriate cell for the circuit in the 'Remarks' column (column 25) of the schedule"

So it doesn't state you must record the 100% value, only that if it isn't from BS 7671 that you state where you got it from.
 
What the foot note on the model form says is...

"Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in chapter 41 of this standard, state the source of the data in the appropriate cell for the circuit in the 'Remarks' column (column 25) of the schedule"

So it doesn't state you must record the 100% value, only that if it isn't from BS 7671 that you state where you got it from.

But must comply with 7671.
 
But must comply with 7671.

Yeah, but I've just looked and I can't find anything in the regs that stipulates you record the 100% value. Just that footnote which stipulates if it's not from BS 7671 you state where it is from.

If you multiply a value from the tables by 80%, the source of the value is still the standard.

I said earlier I record 80%... I do because it's the default in NAPIT Desktop which I use for doing EICs and EICRs, you can change it, but the cert then includes markup to show whether it's the 100% value or the 80% value.

It's how I was taught when I did C+G 2932, 2394 and 2395 a couple of years ago.
 
Well the little chart I chopped up & used for the 80% figures, now excludes the preamble I previously mentioned, but it does mention App 14. Which I've just read, and haven't the scooby what its on about.

But I guess its you can do some maths, or just use the table.
 
Well if you consider the formula for compliance is zs x Ia < Uo x cmin we must have to use the maximum zs value for that OCPD given in appendix 3 ie for a 32 amp type B 1.37 ohms
 
Anyways, just as an aside, been called across to my vacant house up for sale. Neighbour has just had a small fire, FB in attendance. Water everywhere. Laptop in upstairs bedroom appears to be the culprit.

Too high Zs values, or dodgy lithium batteries?
 

Reply to Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Following on from another thread on here, can you please help me with a fundamental issue regarding certification bodies. Bear in mind we are new...
Replies
11
Views
2K
Hi all. I am collecting evidence for a report on the current 'strategy' and trust given to the competent person schemes by the Communities and...
Replies
13
Views
2K
D
Hi I was wondering if anyone could fill me in here. I tested an installation for someone which consisted of 2 circuits to a loft conversion I...
Replies
4
Views
937
NJG28
N
Hi guys i know this has been done do death, i have searched but i've not been able to find an answer. I'm having a mental block so just thought...
Replies
5
Views
2K
Hi guys, im new to this forum so go easy please ;) I am 17Th Ed and Part P Accredited. Have been doing electrical work for years ( commercial...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock