Table 41.3 is max Zs for breakers to 60898 for 0.4 and 5s disconnection time including the overcurrent characteristic of an RCBO i.e the MCB part of it which must comply with these values.

Thats my take on it anyway, the values relate to the overcurrent (MCB) part of the RCBO i.e 6A 30mA, 16A 30mA 20A 30mA etc.
 
Last edited by a moderator:
Well, having just got hold of my brb, it clearly states under the tables:

"The circuit loop impedances given in the table should not be exceeded........."


Mind you, flicking over the page, reg 411.4.9 kind of contradicts the whole theory??

Does my head in:confused:
 
Last edited by a moderator:
Yep it's full of contradictions. OSG table 2D page 103 shows maximum Zs for 0.1 to 5 second disconnection times for circuit breakers BS3871, BS60898 & RCBO BS61009 and the values are different to big red!
 
The OSG has a 1.24 correction factor applied as to big red as stated on page 100 of OSG under "note" for temperature differences, thats why OSG and big red differ.

Tables 41.2(fuses) 41.3(breakers & RCBO's) 41.4(fuses) are impedance values under TN supplies headed on page 47 411.4 - TN systems

Table 41.5 are impedance values for TT supply headed on page 50 411.5 - TT system

and page 51 411.6 - IT system


Thats the way I see it


Ray
 
411.4 is for TN systems,
411.4.9 says table 41.5 can be used to satisfy 411.3.2.2

Although note should be taken of 411.5.4
Which also limits the max Zs.
 
No. What i said was "Table 41.3 only states overcurrent characteristics of RCBOs not earth fault loop impedances as in 41.5." thats table 41.5. Any way i don't understand how the tables on pages 48,49 and are not for TNS & TNC-S systems as well.Taking what raylewis says that the OSG values have a correction factor from the big red Tables 41.2(fuses) 41.3(breakers & RCBO's) 41.4(fuses) which i agree is correct (sorry missed the note on page 100 OSG) then firstly where are the tables for TNS and TNC-S systems in the big red? and why are the corrected values in the OSG table 2D correct for TNS & TNC-S when they have been take from Tables 41.2(fuses) 41.3(breakers & RCBO's) 41.4(fuses) in the big red? Sorry i just don't get it!
 

Reply to Max zs on rcbo in the Australia area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
0
Views
860
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock