Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?
Discuss Max zs readings for TT in the UK Electrical Forum area at ElectriciansForums.net
Depends on the rcd used for fault protection ie 500mA,300,100,30?Hi just wondering what people are noting as there max permitted zs reading on test results sheet for TT systems? 200ohms or 1667ohms?
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).Max Zs permitted is the maximum value that the OCPD need to trip. It is not the DNO value or the 200 ohm stable value.
You do hear a lot of different things on this, a lot of people simply don't accept what the BBB says. But it does say that so that's the values we have to use when compiling a cert.I was thinking it had to be 1667 if 30mA 500 for 100mA etc as that is what it says on 41.5 but I was hearing different things.
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.
I was thinking thayJust realised that this thread was about Zs not Ze or Ra..
My comment about the DNO figure of <200 was Ze..
No you didn't.Yeah that is what I said
I go by what the dno insist on and the only figure that is realistically acceptable <200
Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?
If you enquire a DNO will give you a figure of 21ohms max for their side of things.
Really and no 1667?If it helps the NICEIC online certification gives you 200 as the autofill value to select on their forms