In preparation of wiring up a commercial premises (function rooms / bars / restaurant area) I am trying to determine to what extent the existing 60A single phase supply might need upgrading. I have not had to do this myself for a commercial premises, and I am wondering if the same rules apply as a domestic property.

There is a substantial increase in the previous demand, as the building is being extended and will now do food (previously no cooking appliances).

Having contacted the company which is going to supply much of the equipment, i know the following loading (at least)! and all single phase-

Dishwasher 3kW
Fryer 6kW
Grill 3kW
Cold room '13A Supply'
Combi oven '13A Supply'
Fridge-counter 2kW
Hot cupboard 1.5kW
Overshelf 1.2kW
Dumb waiter '8A start up', apparantly
Instantaneous water heater 10kW

There are 3x small bars (so associated cellar gear- unknown)
I have been advised that the heating system will demand around 22A.
For lighting there will be around 220 SES or similar lamp holders in operation (unknown wattage but most must be dimmable, mostly fancy wall lights and chandeliers) it is very possible that all rooms will be in use at the same time
10 LED downlights (unknown wattage)
6x 70W SON wall washers
Around 30x 28W 2D type fittings
Around 20 standard maintained & NM emergency bulkheads or exit boxes
5x 1.8kW hand dryers, how does diversity apply?

Any help is much appreciated. I've never had to calculate this type of installation.

I have been advised by the plumber that it is very possible that another electric water heater will be installed but not set in stone.
 
There will of course be a few additional loadings but nothing substantial (3x tills, CCTV, FA, 4x TVs, perhaps 3x rings but will only be generally used to plug a hoover in or christmas tree lights) Hmm
 
According to the on site guide, Theres very little room for diversity because it is commercial!

I'm sure lighting is 90% of total
an 100% for everything else

Dave
 
That sounds like a lot of demand on a 60A SP&N system. How much room have you to manoeuvre? Is it reasonable to consider upgrading to three phase?
 
According to the on site guide, Theres very little room for diversity because it is commercial!

I'm sure lighting is 90% of total
an 100% for everything else

Dave


If you want to get a realistic Max Demand value for this commercial installation (or any other type of installation) the very last guides you want to use is BS7671 or any of it's guides!! Not unless you want to pay for a grossly oversized installation!!


OKay now back to the real world of reality, ...A new DNO 80A/100A 3 phase supply should more than cover these loads the OP has provided us with above, ...and any sensible future upgrades, that may be needed to tweak this businesses needs!!
 
Ok so what is the rule of thumb you use for a more realistic max demand for
domestic?
commercial?

and what do you use for ELCs

Thanks Dave
 
one of my clients is a country pub. the kitchen alone pulls 100A when they are doing food. 3 phase was not an option as the nearest 3 phase was 3 miles away. he had a single phase upgrade to 180A.
 

Reply to Maximum demand / diversity (commercial) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
A couple of questions for you. The electrician that rewired our house ran a 10mm2 SWA to our outbuilding. The total length of the cable is about...
Replies
17
Views
4K
I have been asked to do some work on a large 25 room mini mansion spread over 3 old properties made in to 1 with 6 consumer units on a single...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock