Discuss Maximum tolerable fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

T

TALK

Just completing the testing of a transportable catering unit.(chip van). Within the NICEIC REPORT I must complete,

a.MAXIMUM TOLERABLE FAULT CURRENT(is the same as PSCC)?

b.MAXIMUM TOLERABLE UPSTREAM ELI.(is this the same as Zs)?

If so how do I achieve these values when the Power Transformer/Generator is different at every site,or would this mean a report must be completed at every site,every time the catering unit moves.

This unit moves 3 times a week.

Thanks for your help.
 
I would suggest that maximum tolerable fault current refers to the maximum before damage occurs.
So if the connection is made direct into the unit's CU, which should be rated at 16kA, the maximum tolerable fault current would be 16kA.
Whereas if the connection is made via a plug and socket rated at 6kA, the maximum tolerable fault current would be 6kA.
This would be PFC.
The maximum tolerable upstream ELI would be the maximum Ze that the unit can be connected to and still allow ADS to be achieved.
For instance if yout unit just had lighting on a 6A type B MCB, the maximum Zs would be 7.67Ω. If the resistance of the unit's wiring between the connection point and the furthest lighting point was 1Ω, the the maximum tolerable upstream ELI would be 6.67Ω.
If however the unit had both lighting and socket-outlets, and the socket-outlets were protected by a 16A type B MCB, the maximum Zs would be 2.87Ω. If the unit's wiring was again 1Ω, then the maximum tolerable upstream ELI would be only 1.87Ω.
 
Last edited by a moderator:
well put spin, clear and concise. better than i could have explained it.
 

Reply to Maximum tolerable fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Like a host of UK residents recently (230% increase in genny sales apparently), I've just invested in a small (3500W) portable, dual fuel...
Replies
12
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock