Discuss MCB -> RCBO I'm missing something silly in the UK Electrical Forum area at ElectriciansForums.net

Thank you all for the suggestions.
I'm 100% I had the right live and neutral.
Now I've remember that mid-point I turned a fan isolator off and never turned it back on I'm hoping that will turn out to be the easy answer.
The shared Live is a great shout, and it's conceivable that the switch positions led to the differing results. I'll hold that thought in reserve.
(Btw when I said R1+R2 above I meant continuity tests involving the Neutral.... )
 
Simple job, swap an MCB to an RCBO on a lighting circuit. It's got me totally stumped!

IR test L+N -> E is fine on the circuit. So is Zs. All 2-way switches operated.
Instant trip when changed to RCBO though, and tried two RCBO's
Ramp tested them both, all good. All tests pass on them with no load.

Also (in desperation, shhh!) tried connecting lighting circuit via plugtop / flex / wago's into a socket from the RCD side of the board. It didn't trip (and works). Then tested that RCD - all good.

My brain gave up at that point. I initially wanted to say there's a shared neutral with something on the RCD side of the board.
But if there was that would trip the RCD side when the circuit was on an MCB the unprotected side...

All I could think of was incredible coincidence of two strangely duff RCBO's that pass all tests until there's a load on, or a strange transient fault?
Now had to put back MCB and carry on with day.
Going back tomorrow, any thoughts of other helpful tests or recollections of more unusual faults welcomed!
(it's always things you plan to be quick that go pear shaped.....!)
Borrowed N
 

Reply to MCB -> RCBO I'm missing something silly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
915
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
792
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
418
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
874
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
528

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock