- Reaction score
- 3,129
You don’t discriminate RCDs on the mA trip current, you discriminate on the basis of time.
That is what time delay RCDs are for.
That is what time delay RCDs are for.
Discuss MCCB with RCD settings in the UK Electrical Forum area at ElectriciansForums.net
It’s at 1Out of interest,what did you set the delay,to?
???Has anyone set one up before and could tell me? Or know how to
It’s the bottom dial I can’t understand? So it just works on disconnection time but in milliseconds? So say I have no greater than 32A final circuits on TT which is 0.2 seconds then what do I set it?It's a wind up this one. Guaranteed
Ok so it’s TT, in this panel you have Main MCCB/RCD one in picture then 3 X BS88 fuses which feed some electric boxes with 16A sockets with relevant 30mA RCBOsBut you were asking what delay a TT circuit should be set to. Are you saying you know this, but need to convert seconds to milliseconds?
To answer that, there are 1000mS in a Second.
Thanks is there a way to understand how to set the time delay?It is a variable earth leakage modual that is used with a mccb eather bolted on or using a shunt trip module
The top part is to set trip current
Bottom is to set a time delay
They are mainly used on sub circuits or large motors ect were the time delay can offer some sort of discrimination
Remember earth leakage is cumulative
Thanks is there a way to understand how to set the time delay?It is a variable earth leakage modual that is used with a mccb eather bolted on or using a shunt trip module
The top part is to set trip current
Bottom is to set a time delay
They are mainly used on sub circuits or large motors ect were the time delay can offer some sort of discrimination
Remember earth leakage is cumulative
I’m not sure what the regs require? I know how to set trip current but not the trip delayI'm still confused. Do you not know what the regs require, or do you not get the seconds/milliseconds thing?
It’s TT system so this is the upfront RCD, all there is down stream is 30mA RCBOs at boxes protecting socketsFirst you need to know what function it is required for. Secondly you need to consider upstream devices and how they are operating then the vigi module can be set to ensure coordination is achieved.
No, of course not.So my final circuits are no greater than 32A on TT which is 0.2 seconds so I can set the trip delay to 0.3
Reply to MCCB with RCD settings in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.