Hi all,

Just after a bit of advice from all you domestic installers out there.

I've been asked to do a job in a house which involves running a cable in a wall. The cable needs to run vertical the entire height of the wall. However I cannot run it where the walls meet at an angle due to obstructions. This wall is at the base of stairs so quite small.

Can I utilise the thermostate as an acessory and run behind it (obviously taking it off wall and mounting back on after filled) to fullfill the requirementof running to an accessory. Or is this not allowed as it isn't actually supplying the accessory.

If not can I just cap the cable with metal capping at least 3mm thick. I know meeting the requirement to prevent nail penetration is hard to meet.

The circuit is covered by a 30ma rcd. Just a little confused as my domestic regs knowledge is not up to scratch. Don't want to install a cable unsafeley.

Any advice would be appreciated. Thanks
 
the thermostat is an accessory and assuming it has a LV supply, then it can serve as a pointer for a prescribed zone. won't do if it's a wireless stast.
 
It's definitely Lv. There's surface trunking supplying it. Was even thinking I could bury these supply cables as well If pos. Get rid of the unsightly trunking. What do ya think?
 
go for it. but remenber thst buried cables need RCD protection.
 
There is no requirement in BS7671 for mechanical protection to be earthed.
So not a sweeping generalisation, a simple statement of fact.
 
Last edited by a moderator:
I'd be dubious about running it using a supposed safe zone from a room thermostat that itself has got surface mounted cable. The room stat is something that's likely to get moved / replaced at some stage, and anyone would assume that the only cable run to it / likely to be in that safe zone would be the one that's surface mounted.

technically it's arguable, but going with the spirit of the regs, it wouldn't seem a wise move to me.
 
There is no requirement in BS7671 for mechanical protection to be earthed.
So not a sweeping generalisation, a simple statement of fact.

Steel conduit and trunking are mechanical protection and require earthing
Any mechanical protection which is an extraneous part needs to be bonded
 
Last edited:
Steel conduit and trunking are mechanical protection and require earthing
And mechanical protection which is an extraneous part needs to be bonded

how's it an extraneous conductive part if it's buried in the wall?

mechanical protection and earthed metal capping are 2 separate protective measures, it doesn't need to be earthed as long as it actually does provide protection against nail penetration.
 
how's it an extraneous conductive part if it's buried in the wall?

mechanical protection and earthed metal capping are 2 separate protective measures, it doesn't need to be earthed as long as it actually does provide protection against nail penetration.

He made a blanket statement about mechanical protection, nothing specific about it being buried in anything
 
It doesn't matter whether it's buried or not, there is no requirement in BS7671 for mechanical protection to be earthed.
You want to earth it carry on, I'll get you some PVC conduit to earth.
 
It doesn't matter whether it's buried or not, there is no requirement in BS7671 for mechanical protection to be earthed.
You want to earth it carry on, I'll get you some PVC conduit to earth.

Wtf? Steel conduit and trunking is mechanical protection and I'm pretty damned sure it requires earthing.
 
Mechanical protection is not required to be earthed.

That is a sweeping statement Spin, you've just told the op and anyone else reading this, including trainees and diy'ers that you never need to earth mechanical protection regardless of the situation which is not true.

As it happens, in this case the way I read it is that one option being considered is to run the cable in the wall outside of a safe zone with a metal covering.

In this case the mechanical protection does need to be earthed.
 
That is a sweeping statement Spin, you've just told the op and anyone else reading this, including trainees and diy'ers that you never need to earth mechanical protection regardless of the situation which is not true.

As it happens, in this case the way I read it is that one option being considered is to run the cable in the wall outside of a safe zone with a metal covering.

In this case the mechanical protection does need to be earthed.

I can see where he's going with it, but it didn't come across right.
In your example it will depend on the type of mechanical protection. Steel conduit would need earthing, but a solid steel plate resistant to penetration by nails etc likely wouldn't need it
 
The reg dealing with cables buried in walls mentions various scenarios from >50mm and several 'ors' but the ones mentioning metallic protection all say earthed.

It's the statement 'There's no requirement in bs7671 for mechanical protection to be earthed' that I find misleading.
 

Reply to Mechanical protection/ Safe zones in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
838
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Hi All I’m after some advice, I am doing a restaurant fit out involving a number tables that have hot pots built into the table, for customers to...
Replies
19
Views
2K
I'm renovating a property and vaulting a kitchen ceiling to gain more head height. The floor will be a slab which is yet to be laid. Would it be...
Replies
5
Views
3K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock