Discuss Megger 1552 vs Fluke 1652 vs Metrel 3100 in the Electrical Tools and Products area at ElectriciansForums.net

B

brman

Ok, yes I know there are 1000s of posts on which tester is best but my brain is starting to fry with all the options so I'd really love someone to sanity check what I am thinking....

My problem is that I have used all three of these testers but only for specific tasks and I am not experienced with these measurements so am likely to miss stuff. I am on a budget and happy to consider secondhand but do have some concerns with buying sight unseen on ebay and also need to consider cal costs, knackered leads etc. So....

Megger 1552: I have used one of these for all the basic tests (ie. continuity, loop tests, resistance, RCDs etc). I liked it - it is solid,easy to understand and most tests (eg cont and loop) don't need you to press the start button. On the other hand RCD tests could be a pain as it has no auto mode.

New is outside my price range but there are plenty on ebay going for around £300 so the only real problem is my reservations of buying on ebay.

Fluke 1652: I've been offered a 2nd hand one by a mate for £300. I've not seen it yet but supposedly all the bits are there, it is good nick but the cal ran out recently. I've only used one for RCD testing (which was easy enough and has auto test) and it looks a solid bit of kit but I did notice a colleague swearing when he was using it as he was getting variable continuity measurements (constantly having to re-null) and needed 3 hands to hold the probes and press the test button. There again they didn't have the probe with a test button which I assume solves that problem?

Metrel 3100: I've gone for this over the 3000 as I have had a brief play with one (RCD testing again) and it had the remote commander. To me this looks pretty important but what do you more experienced guys think?
The big plus on this is that I could afford a new one so no warranty or cal problems.

I guess my first question is am I right in assuming all these will do everything I'll need for standard jobs (if there is such a thing!)?

I got the impression that the order of preference here is probably Megger->Fluke->Metrel but would the supposedly superiority of a 2nd hand megger outweight the advantage of going new with the metrel? Particularly as the Metrel appears to do a fair bit more.
And are all those extra features really useful on the metrel? I am perfectly capable of looking up fuses etc in the book so I don't really need the tester to do that for me.
And where would you put a known good but 2nd hand Fluke in all this? Does £300 sound a reasonable price?

Any pointers very welcome before I spend all my hard earned....

btw. I should add that I doubt I will be doing major electrical installation work and I am not even 100% sure I will be going the full self certification route (I may end up calling in a more experienced pro on more complex jobs anyway) but I do want the ability to fully check installations I work on and also ensure anything I do is up to scratch, even if it is not notifiable.

Toby
 
Yes, and I have read most of it. Trouble is, as far as I can tell it just shows that people have their preferences based on what they are used to and what problems they have had. And value judgements are based on new prices.

I guess I was more interested in what people think about buying 2nd hand, particularly on ebay, and whether they would really go that route to get a prefered tester rather than new with something like the Metrel.
My problem is that I am just not experienced enough to know what is most important in a tester. In my limited experience they all have limitations and can give different results. For example in RCD testing I found back to back testing (on the same RCD) gave significantly different results on the 3 testers. There again, all the results were good so perhaps I should not stress about that?

Toby
 
Hi Brman, i don't know if your funds would stretch to a megger 1553, but that does have an auto rcd test function which seems to work well.
 
hmm... I have to admit I hadn't thought to look further up the megger range. A quick check on ebay suggests I would probably pay £100 more for one (2nd had of course) which would be do-able. Not so many listed though.
Is the general consensus that auto RCD test is important, or is it just a time thing?
 
oh dear ... I am starting to think I have mixed up the 1502 and 1552.:blush5: I think it might be the 1502 I have used.

So the 1552 is looking a good option then as I liked the 1502 apart from the lack of auto rcd. Only trouble is finding a decent 2nd hand one....

Thanks
Toby
 
Lenny, I guess my budget is £400ish all in (ie. inc vat) so I would already be pushing it with a new Metrel 3100 but that would make the Dilog ok too.
Can you compare the Dilog to the metrel quality wise?

Toby
 
Can I just add that IMO you should allow for calabration (unless cert with unit) and a set of leads if buying second hand. So if it needs both that another £100 on the SH price right there. The leads may be ok but they are the only thing I replace on my 1651 - besides batteries :)

Hope that helps.
 
Thanks DaveyD. That certainly concerns me. So the fluke at £300 might be good value but only if I am sure the leads are good. IIRC my mate told me he paid £60 locally for a calibration so I need to factor that in.

I am starting to think I should go for the fluke only if it and the leads look in very good nick and perhaps do some continuity tests to check the low resistance measurements are consistant?

Otherwise I might play it safe and go for a new Metcal 3100 or investigate the dialog Lenny mentions.

Toby
 
spinlondon. I tried that but you are right, most of them do what I need. It did show up another cheap option the Idea Suretest but I struggle to find any comments from anyone who has owned one.

Toby
 
The new fluke is faster at doing zs's than the megger we have both at work but the megger automatically presses test for you , but u also get a lead with both ( a line lead) which has a test button on it- the megger one also has a torch button on the probe!
 
I'm in the same position and trying to choose my first test kit (god, that sounds like a Fisher Price toy!).

Decided to go for the Metrel 3000. It's got all the features I need, without too many additional things to confuse me.

Made the decision after a chat with a guy at Test Meters, Electrical Testing Equipment & Measurement Instruments. Very helpful and worth the phonecall, they didn't try to push me into buying a more expensive bit of kit, just made suggestions.

I've decided not to get the Metrel 3100 as it's more expensive and I've been told the tip-commander probe is a bit bulky at times.

Additionally, the 3100 gives a clear pass/fail readout for some tests, whereas the 3000 just gives the value measured. As a newbie, it's probably best that I get used to checking the readings against regs and make my own mind up, rather than relying on the machine.
 
Megger wins hands down for me.

2 leads for Loop test and you dont have to press a button.
continuity test - no button again
3 phase fault current testing

The Fluke is okay but it is easy to have it on the wrong setting ( i'm thinking about Pscc and Pefc tests)
The Flukes buttons are not as solid and the screen is cluttered.

One thought, why do you need RCD auto test? My megger is the 1502 and it doesnt have auto test, but I've never needed it. I just test at the RCD.
 
With the auto test, you can plug the unit into the first socket, press test then stand by the CU, and just flick the RCD back on untill it stops tripping.
Then go back to the machine, and all the results are there on the screen.
 
and that is standard on the 1552. works a treat, just as spin describes.
 
Tigerpaul: I think those are the things that draw me to the megger. The autotest does appeal as it makes it easy and I keep on hearing it means less walking back and forwards but I have to admit I can't see why I shouldn't just stay at the CCU as you say. On the other hand the simplicity of just plugging into a socket does appeal given the hassle I found with the croc clips and trying to get a reliable connection.
I guess with the megger I still have the choice of the 1502 without and the 1552 with autotest.

DNS1: if I do go for new then talking to test-meter.co.uk first does sound like a good plan.

Thanks for all the comments guys, it is making it clearer in my head even if I haven't made the decision yet.

Toby
 
In time I'll probably get a Megger myself, but for starting out I'm going with the Metrel. I can't afford the Megger right now and besides, when it comes to upgrade time, there will undoubtedly be newer Meggers out with even more features and newer technology.

Let us know what you end up with.
 
dcf: I assume the 3120 is one up from the 3100? Has it got download or something?

DNS1: I'll certainly report back. At the moment I am tempted by the fluke my mate is selling just because it is easy to go and check it out. if that doesn't work out I'll probably look out for a decent condition megger 1552 2nd hand, failing that the metrel new is a safe option.

Toby
 
Oops my mistake make that a3125 combo lite.as I say good for the money.ramp tests at 0 and 180 degrees.auto tests rcd as well
 
In time I'll probably get a Megger myself, but for starting out I'm going with the Metrel. I can't afford the Megger right now and besides, when it comes to upgrade time, there will undoubtedly be newer Meggers out with even more features and newer technology.

Let us know what you end up with.

Not necessarily better Meggers, currently the proven and reliable old MFT15xx series a better choice than the new all singing, all dancing, half-baked MFT17xx series.
 
spinlondon. I tried that but you are right, most of them do what I need. It did show up another cheap option the Idea Suretest but I struggle to find any comments from anyone who has owned one.

Toby

You need to go on an American site to get any reliable feedback from Ideal Suretest owners as they have had it available for a lot longer than we have in the UK.
 

Reply to Megger 1552 vs Fluke 1652 vs Metrel 3100 in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi I’m just starting to do ev chargers so it’s looks like I need new tester. I currently have Megger 1711. So I can’t do a 6ma rcddc test. I...
Replies
3
Views
787
Chaps - having problems with a new Megger MIT420/2 insulation/continuity tester 'oscillating' and failing to give stable resistance readings in...
Replies
2
Views
653
I saw a Fluke 1653B on Gumtree local to me being sold as faulty. Fault was stated as no continuity between 'N' and 'PE' ports on the resistance...
Replies
3
Views
495
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
12
Views
4K
Hi I purchased my Megger X1 in July last year so only 7 months old, having been a Megger fan for 20 Years... I've now had the opportunity to get...
Replies
1
Views
617

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock