Discuss Megger MFT PFC error message in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
I used a friends Megger today and we both came up with an error he hasn't seen before.

We was performing a PFC test at the imcoming of a new DB.

Leads were in line and neutral ports and tester set to L-N, 2 lead test, Zmax.

As soon as you make the connection the tester beeped and flashed <PE>

We managed to get a reading but he didn't know what the error meant. Searching the internet doesn't seem to bring up much
 
(pure speculation , does it want a PE reference to
confirm "polarity" )
...No I have yet to read that Meggers Instructions..
( So many "features" ... n-tweakable-settings
can get in the way sometimes )
 
Can testers differentiate between an incorrect connection between N and E on a TN system assuming that is what it is.
I honestly don't know, just throwing an idea in the really confuse the mix... :D
 
Can testers differentiate between an incorrect connection between N and E on a TN system assuming that is what it is.

Not with a 2 wire test they can't.

An they wouldn't really be able to prove a fault with 3 wire testing, but could flag a possible warning message if the resistance of one was out of a pre defined tolerance set in the tester.

I believe the <PE> fault you have seen, is an issue where it detects the touch voltage rising on a conductor above safe limits.

This could point to a fault on the DNO side of things, although only speculation. Call Megger an find out what the code means.

Edit: New batteries in the tester? Or if rechargeable, they weren't low?
 
Last edited by a moderator:
as Rob suggests, it would seem that PE would indicate a voltage on the PE. however, OP says he was using 2 leads L-N. possibly be a N not tied down to E due to a poor connection. I found 1 of those causing a high Ze. turned out the jumper from N-E in a PME head was loose.
 
as Rob suggests, it would seem that PE would indicate a voltage on the PE. however, OP says he was using 2 leads L-N. possibly be a N not tied down to E due to a poor connection. I found 1 of those causing a high Ze. turned out the jumper from N-E in a PME head was loose.

This was my initial thought too.

Although a call to Megger an probably some more testing will be required.
 

Reply to Megger MFT PFC error message in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
605
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Hi have had the megger 1741 MFT. Error code 140 has appeared on the tester which is a fault on the circuit board for the 3 lead low zs test This...
Replies
7
Views
9K
Megger MFT1730 with Bluetooth. Calibrated until sept 2018: Used, but great condition. Comes with all accessories. Wanting £600 Ono Some spec...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock