Discuss MEM RCD failure? in the UK Electrical Forum area at ElectriciansForums.net

S

sirocco

I have a split MEM2000 board (15+ years old) with four circuits each with MCBs protected by a single 100A 30ma RCD.
The RCD has been tripping out over the last 4 days at increasingly more frequent intervals (initially evry 6-8 hrs now it holds for about 30mins)
It trips with the mcbs on the four circuits switched off! Does this automatically infer that the RCD is defective and should be replaced or are there other checks that should be made?
Frustrated! any advice welcome.
Graham
 
What results did you get on your ramp rest and 1x & 5x tests?
 
Disconnect your live conductors on the rcd side including the neutrals.am sure rcd wil stay up. Connect one circuit at a time will probably trip when you connect faulty circuit but it could be other of number of things ie faulty appliance etc try in plugging everything as wel It may help
 
Thanks for all the replies, the cause was an overloaded 6 way extension lead which has now been binned and replaced. What I have learnt is that going forwards the CU will be replaced (probably Wylex) with RCBO's on circuits which need protection.
I have costed out that an 8 way ,fully populated, box works out cheaper than a couple of MEM rcbos, and much easier to source/maintain.
However the ditching of a cheapo ext lead will do for know!.
Cheers
Graham
 

Reply to MEM RCD failure? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
767
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hello everyone, I'm newly registered having read the boards from the shadows for a while. I have a question about neutral to earth faults and...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock