Discuss Neutral to earth fault affecting both RCDs in the UK Electrical Forum area at ElectriciansForums.net

Zs was 0.4, on the circuit I was installing the extractor on.

With regards to leads, no I haven't replaced them yet, I will look at picking up a set if I can't seem to find a solution on the system itself, I haven't had them that long but it's a good suggestion for me to look into, thank you
 
I was reading someones explanation and what I took from it was that the amount of current lost from the neutral was less than 30mA and therefore not triggering the RCD... Didn't fully understand how that happens though.

Ah that makes sense for why that fault didn't cause the RCD to trip, I was thinking more of a direct short from a screw or the like but you're right it could be a lot lower than 1M and not trip I suppose. Assuming in most cases a 30mA RCD's only operate above 20mA..... 230V/0.02A=11.5kohm. Any chance something could be wet?

Hopefully checking your leads and using a long lead to check the earths should identify the problem with the RCD test.
 
Ah that makes sense for why that fault didn't cause the RCD to trip, I was thinking more of a direct short from a screw or the like but you're right it could be a lot lower than 1M and not trip I suppose. Assuming in most cases a 30mA RCD's only operate above 20mA..... 230V/0.02A=11.5kohm. Any chance something could be wet?

Hopefully checking your leads and using a long lead to check the earths should identify the problem with the RCD test.
Yes possibly, there is an external wall that the faulty cable is buried on if there's water from the outside I suppose it could be wet but I would probably expect to see that on the plaster on the I side. Will get the damp meter on it next time, thanks
 
To clarify with certainty:

An N-E fault downstream of an RCD can cause it to fail a test. because some of the leakage current generated by the tester can 'get back into' the neutral via the fault and go back through the RCD, hence reducing the imbalance. Equally, the N-E fault can defeat the RCD's own test button, because that might simply send some current from the L-in terminal to the N-out terminal, only for it then to disappear down into the CPC via the fault without returning through the RCD to create the imbalance.

But this only happens on circuits protected by the RCD in question. An N-E fault on a circuit protected by a different RCD won't affect the first one. That is logical: N & E are always connected together upstream of the RCD anyhow, whether at the origin (TN-C-S) or the substation (TN-S) so it doesn't matter if they are also connected at an upstream fault.

What can happen that 'crosses over' from circuits on one RCD to another, is the effect of a heavy load current showing up an N-E fault and causing a trip. In that case, it doesn't matter where the load is, whether on the RCD that trips or another. Anything that creates voltage drop in the supply neutral can raise the N-E voltage and drive current through the fault. The fault will however always be on the one that trips.
 
Last edited:

Reply to Neutral to earth fault affecting both RCDs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
393

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock