Discuss metal board on tt system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It doesnt...but logically if supply tails which are not RCD protected pass through the metal enclosure the high Zs on a TT will not enable the protective device to operate if the tails short onto the enclosure...therefore it will not comply with the required disconnection time.....Metal enclosures can be used if the tails are RCD protected,or if measures are taken to ensure the tails cannot short onto the enclosure,such as insulated bushes and clamping the tails to ensure they are secure and cant move.
Generally it is easier and preferable to use an insulated enclosure.
 

Reply to metal board on tt system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
980
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
997
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
554
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock