Hi Guys

Yes, me again, heres the scenario, customer calls in and they say the property is empty and there has been some units recorded on the meter, we install a check meter and shows the meter to be accurate. I have heard of electrical leakage, not sure if thats the right way to describe it.

The question is how do I explain this to them in an easy way ? And how would an electrician test for this leakage.
 
Leakage in the conventional sense comes from two main sources; resistive leakage due to insulation resistance that is less than infinite, and capacitive leakage from cable capacitance and suppressors in equipment that is connected but switched off. Neither is likely to register on a meter, unless something is seriously amiss.

Capacitive leakage has near zero power factor, so although it can clock up a few milliamps in a large domestic installation resulting in one or two VA being consumed, the real power is more likely to be in the order of a few tens of milliwatts.

Resistive leakage on a system with barely acceptable insulation, say 1MΩ from L-E and L-N, will pass 2x230/1M = 0.5mA, for a power consumption of 230x0.0005 = 100mW. It would take 10,000 hours (417 days) to consume one unit (kWh).

Therefore it is likely to be actual equipment that is consuming the power, such as the aerial amplifier mentioned above, rather than the fabric of the electrical installation. If you were registering one unit per week the load you are looking for would be 1000/(7x24) = 6W, which is typical for a small electronic device that gets mildly warm in use.
 
with the main isolator OFF and the circuit breakers turned on,
Check voltage is 0v on the outgoing L-N of the main isolator.
then check resistance between L-N of the same terminals, if there is nothing switched on then it will read open circuit.
I suspect there will be something drawing power. heating timer, outside light on pir, smoke alarms etc.
 
Leakage in the conventional sense comes from two main sources; resistive leakage due to insulation resistance that is less than infinite, and capacitive leakage from cable capacitance and suppressors in equipment that is connected but switched off. Neither is likely to register on a meter, unless something is seriously amiss.

Capacitive leakage has near zero power factor, so although it can clock up a few milliamps in a large domestic installation resulting in one or two VA being consumed, the real power is more likely to be in the order of a few tens of milliwatts.

Resistive leakage on a system with barely acceptable insulation, say 1MΩ from L-E and L-N, will pass 2x230/1M = 0.5mA, for a power consumption of 230x0.0005 = 100mW. It would take 10,000 hours (417 days) to consume one unit (kWh).

Therefore it is likely to be actual equipment that is consuming the power, such as the aerial amplifier mentioned above, rather than the fabric of the electrical installation. If you were registering one unit per week the load you are looking for would be 1000/(7x24) = 6W, which is typical for a small electronic device that gets mildly warm in use.
Shut up Lucien, don't complicate the issue:tongue::tongue: lol, in fun, please take it as such.
 
Hi Guys

Yes, me again, heres the scenario, customer calls in and they say the property is empty and there has been some units recorded on the meter, we install a check meter and shows the meter to be accurate. I have heard of electrical leakage, not sure if thats the right way to describe it.

The question is how do I explain this to them in an easy way ? And how would an electrician test for this leakage.

Maybe give us an idea of the of the recorded usage both meters are showing?
 
I didn't say anything Pete. Can't talk and chew stub sleeving at the same time :)

check resistance between L-N of the same terminals, if there is nothing switched on then it will read open circuit.

Not always true for small electronic items. Loads that use a capacitive dropper read O/C to a DC resistance test as do some small SMPSUs, but consume current on AC mains.
 

Reply to Meter Accuracy - leakage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
452
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
1
Views
955
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock