I had an eicr done recently, the electrician gave a C2 for the meter tails having their outer insulation stripped back too far.

Can I take a piece of the grey insulation off a spare tail and cut and glue it onto the missing piece to clear the C2? Much easier than having to strip back as it's at the meter.
 

Attachments

  • 20211223_141700.jpg
    132.5 KB · Views: 29
Inform your electricity supplier that your electrician has identified a dangerous fault with your electric meter.

they should fix it free in my opinion.
 
Looking at picture, Call/inform DNO they will send someone or authorise electrician to fix it , (DNO will reseal the cut out ) if its going to isolation switch ....( looks like it is )
 
Is it exposed to touch or is it in a cabinet only accessible by use of a tool / key?

I have seen it argued that if it's the latter then it's a C3.

I wouldn't be busting a gut to fix it either but it should be seen to at some point.
 
C2 by definition is POTENTIALLY DANGEROUS.

if that is what the electrician has reported then if you are renting it out then you have 28 days to get it fixed.
by deferring the problem to the network operator as they are authorised to re terminate to the meter, you will have a paper trail or show that the C2 fault has been repaired.

if you stick some cover over it with glue, you leave yourself wide open for any issues with it. E.g. if the terminals are loose and the cable has pulled out then there could be problems with heat/ arcing .
 
I dont realy see a problem with it. When I was an instalation inspector for the Electricity Board in the early 80s that is the way we were told to do it. Strip the outer insulation back by 12mm to show the inner colour.
 
I dont realy see a problem with it. When I was an instalation inspector for the Electricity Board in the early 80s that is the way we were told to do it. Strip the outer insulation back by 12mm to show the inner colour.
Yeah... but they've had 32 mm stripped back !
 
The meter tails require to have two layers of protection, having so much exposed of the basic installation is an issue for the EICR. If they were behind a barrier or in trunking that would count as additional protection but they aren't.
The exposed parts are between the Isolator and the Henley, I was slightly confused as both sides of the isolator had a seal, however the seal on the output can be removed, the isolator switched off and the tails retrimmed and put back in so that will solve the issue. From the isolator switch onwards in owners equipment so no issue to do it.
Personally I wouldn't have coded it as a C2, the last two EICR made no mention of it or had an issue, but if I want the C2's cleared then I either have to sort it or get someone else who isn't a thorough to redo the EICR
 

Reply to Meter tail insulation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
910
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
970
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
421
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
959
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock