Hey all,
Excuse the ignorance here but I wonder if you lovely folk might have any opinions or better still be able to point in the right direction in the BBB.
I am being asked to move a CU from its current position, behind a fitted kitchen, under the sink and totally inaccessible, except to the countless bottles of Fairy and Pledge etc, that share a home with it.
The meter backs on to it in a recessed box. I need to move the CU all the way down the side of the house, about 8-10m and pop it back on the same wall. I was going to pop an IP65 metal enclosure in the current location and extend all the circuits (actually only 4, thank goodness (or words to that effect!!)) along the outside of the house in singles inside galvy steel trunking. The house has a concrete floor throughout so there's no popping up a board here and there and running the lot along the dirt.
So far, so simple...SO...moving on to the incoming supply side...The meter will now be about 8-10m away from the proposed site for the CU. I normally install a fused switch and then run the appropriate sized armoured (in this case it'll be 25mm) from the FS to the CU. In this instance I was toying with the idea of not doing that but to run meter tails inside the galvy alongside the extended final circuits. Is this acceptable? If not, can you point me in the direct of evidence to this end in the BBB. I have a niggling concern that the DNO only want SWA used to feed CUs or DBs when they're over 3m from the incomers, but for the life of me, I don't know where I go the info...I may even have dreamed it.
Thanks in advance for all your help with this quandry, and obviously thanks too to Pete, who will no doubt point out the fact that I should, in fact, have become a cab driver and left this electricing lark to my betters!! ;-)
 
I’ve seen tails run further than 10 meters under the floor, but I would never contemplate installing it this way myself.
Nothing I remember is in the bbb, but if it’s visibly surface mounted with absolutely no chance of accidental damage maybe in exceptional circumstances this would be ok, but I wouldn’t.

Your call your design.
 
Can you not pull the cables up in the 1st-floor void and join with MF j.boxes to the new position. Or if there is not enough room in the meter box i.e. Tels suggestion install another meter box next to the existing meter box?
 
Have installed tails in Galv trunking before.
Followed the drawing and used 2 inch trunking, then the Forman gave me a length of SWA to strip and use the cores for the tails.
Fortunately the meter connection guy refused to connect and told the foreman to get some proper tails.
 

Reply to Meter Tails in Galvanised Trunking...Is that a thing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
486
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
3K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock