Discuss meters for indivuual rooms- domestic in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
Asked to price a job where a house is getting extended/reno
The owner is going to live in it- and then rent out 2/3 of the rooms

She wants most of the house to be under her meter

Then 2 or 3 of the rooms to be monitored/metered seperately
-by sounds of it she wants them to phyically have to top up- as apposed to just monitor their usage and bill them.

Whats a neat way of doing this in a typical domestic setup
 
The neat way of doing it is to get someone else to do it!

The whole house would be on the single suppliers meter unless you arranged for two incoming supplies and MPANs which would be impractical with the additional costs. You could split the supply and fit a second meter to monitor just the non metered rooms if you wanted but it seems redundant.

Practically it is easiest to run a fuse protected distribution circuit into the rooms to be monitored and fit a MID certified pre payment meter then a board for the rooms lights, power, etc. Messy and inconvenient but possible. It gives full control of the supply to the rooms to the tenant so that no input is required.
 
I had some work from a guy recently who inherited a large hourse and wanted something similar, he wanted each of the 3 rooms he was renting out to be metered to cover power, electric heating and lights. then also the downstairs kitchen/lounge to be metered so he could divide by 3. he was living on the 2 upper floors and was a right penny pincher! I explained the cost of the works and he quickly decided he would just charge them more in rent to cover not just there usage but his own aswell!
 
I had fun disassembling the meters in a house, light and power off the better, I think it took accepted the old 5p and 10p coin and the light fitting had that odd socket that you could plug an electric iron in to.

I think in the past you could set you own tariff within reason, the same as if you install a coin operated phone in the hallway.

I love slum landlords ;o)))))
 

Reply to meters for indivuual rooms- domestic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
453
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi all, Customer has built an annex and their mother lives with them. Separate Board and all wired correctly. She want a separate meter now for...
Replies
0
Views
737

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock