Discuss Metrel TEK118 Earth Bonded Metalwork Lead in the Australia area at ElectriciansForums.net

G

Geordie Spark

Hello everyone, I'm after some help.

I have a Metrel MFT which I bought second hand & has a number of extra bits & pieces with it.

One of these extras is a TEK118 Earth Bonded Metalwork Lead. It's a 4 pole plug which plugs into the MFT, and has 2 leads coming out of it. One lead has a standard 13A plug on the end, and the other has a green croc clip.

The blurb on Metrel's site says: "The TEK 118 is an earth bond lead for testing bonded metalwork or appliances in conjunction with an earth loop tester"


Does anyone know how to use it?

(yes I KNOW I'm a thick Geordie)
All advice gratefully received :dunce:[h=1][/h]
 
Yes

I use it for testing the earthing of bonded metalwork like structural steelwork and bonded pipework

To use it I normally plug it into the MFT put the 13A plug in a socket and connect the croc clip to the metalwork I want to test then press the button :cool4::rolleyes2:
 
Metrel's user guides aren't the best - have you got the disc that came with the tester which has the full user guide? If not call Metrel and I'm sure they will email it to you or show you where it is on their website.

Have fun.
 
Yes

I use it for testing the earthing of bonded metalwork like structural steelwork and bonded pipework

To use it I normally plug it into the MFT put the 13A plug in a socket and connect the croc clip to the metalwork I want to test then press the button :cool4::rolleyes2:

Thank you :)

Is this a live or a dead test & what setting should the meter be on?

Sorry for being thick.
 
Metrel's user guides aren't the best - have you got the disc that came with the tester which has the full user guide? If not call Metrel and I'm sure they will email it to you or show you where it is on their website.

Have fun.

You're right ........... the user guide is diabolical !!!

I don't have the disk - I didn't know there was one - so I'll see about trying to get one from Metrel.

Many thanks for your reply.
 

Reply to Metrel TEK118 Earth Bonded Metalwork Lead in the Australia area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Interesting situation has come up. I have a client who rents out portable toilets - higher end ones with proper flushing toilets/urinals that are...
Replies
7
Views
3K
Hi everyone, So, I live a long way from my mother (8/9) hours... And so I only get to see her intermittently. She has had a fair bit of work done...
Replies
11
Views
3K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
Hi. I am off grid, UK. There is no grid tie or connection and there is currently no potential for connection. Background: I use a Honda EU10i for...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock