Discuss Microsoft excel formula for the adiabatic equation? in the UK Electrical Forum area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
Does anyone know the Microsoft Excel 2010 formula entry to achieve the adiabatic equation?

Where, for example cell A1 is the prospective fault current, cell A2 is the disconnection time, cell A3 is the k factor and cell A5 is the resultant minimum c.p.c size?

Thanks

Spud
 
Does anyone know the Microsoft Excel 2010 formula entry to achieve the adiabatic equation?

Where, for example cell A1 is the prospective fault current, cell A2 is the disconnection time, cell A3 is the k factor and cell A5 is the resultant minimum c.p.c size?

Thanks

Spud

Put this formula in A5:

=SQRT(A1*A1*A2)/A3
 
Im sure there would be plenty of online guides to the basics should you ever want to learn tel. It aint that hard, it's all entirely logical.

i'll have a try, but think i'll be brown bread before i've sussed it. took me a fortnight to learn how to copy and paste without gumming up the keyboard with solvite.
 
You forgot two sets of brackets.

I've used excel for so long I struggle to write conventional formula.

=SQRT(((A1*A1)*A2)/A3)
I tried all the combinations and I already had one additional set fo brackets and found that the answer works each time correctly.
I think Excel is applying Bodmas correctly.
I used =SQRT((A1^2*A2)/A3)
 
I tried all the combinations and I already had one additional set fo brackets and found that the answer works each time correctly.
I think Excel is applying Bodmas correctly.
I used =SQRT((A1^2*A2)/A3)

Unless I'm misreading BGB 543.1.3, don't you take the square root of I²t before dividing by k, not after?
 
I must admit I have now tried the various brackets and got it wrong each time so I do not know what I was doing before.
Last time it worked but this time when I re opened the spreadsheet it was the same as D Skelton's version and the various brackets did not work.
Must have been asleep (or am asleep now):dozey:
 
I'm too set in my ways.

It makes deconstructing formula easier. For complex formula I tend to use hidden cells to calculate small sections then put them together.

Its how I’ve worked for 35 years. I started on Lotus 123, that was a bitch. Before that it was a spreadsheet, a 10' long roll of paper.
 
For complex formula I tend to use hidden cells to calculate small sections then put them together.

Me too, for complex formula this definitely works. It makes calculations easier to tweak this way!

For my accounting spreadsheet for example I have single cell formulae that are hundreds of characters long which can be a PITA to tweak when the need arises!
 
If that's a reply to this:
Unless I'm misreading BGB 543.1.3, don't you take the square root of I²t before dividing by k, not after?

How do others here interpret the formula in the BGB?

S is equal to... the square root of I²t... Which is then divided by k.

In other words, the square root of I²t is divided by k to get S.

k does not form part of the equation which is square rooted.
 
If it gets beyond this then I will break it up.

D34=SQRT(((B37*B37)+(B38*B38)+(B39*B39))-((B37*B38)+(B37*B39)+(B38*B39)))

D34=SQRT(G34-H34)
G34=((B37*B37)+(B38*B38)+(B39*B39))
H34=((B37*B38)+(B37*B39)+(B38*B39))

It all goes back to doing manual spreadsheets, some may find it confusing.
 

Reply to Microsoft excel formula for the adiabatic equation? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Now I know this has probably been covered a few times but I'm struggling to come to terms with my own calculations. I would appreciate it if...
Replies
9
Views
5K
The Ghost
T
hi all small formula issue can anyone help got the basics can add, multiply, ect copy columns, but need a multiple column (sum) entry. Row a item...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock