HI all

I have a problem with a mid position valve that wont move into the heating only position after being in the mid position (i.e. when the water and heating are calling, the water turns off and the valve wont move to the heating only position). The wiring is correct and i have verified it against a y plan wiring diagram (unless of course i am wrong), i wonder if anyone has had this problem? Anything that may cause it (apart from a faulty valve)? I take it all mid position valves are wired the same?
 
99% of the same faults i have been to are a faulty mid position valve
99% of the time you can just replace the head or the motor inside, i always replace the head nowadays

You can test that you have 230v returned from the room stat back to the valve/wiring center and if so then the valve is faulty
In very rare circumstances the ball become detached in the valve and you would then need a plumber to change the mid position valve body

Quick edit

let me know what valve it is as some heads can not be replaced and undoing the screw lets the water out hehe
 
as long as you have the hot water off connection ie; from the cylinder stat and the time clock you should be ok. try a replacement head on the valve
 

Reply to mid position valve issue in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
666
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K
Hello I have a central heating system, with a Y plan layout. The neon indicator on the thermostat seems to be sometimes dimly lit / flickering...
Replies
1
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock