My latest customer asked me a goodun:

He noticed from the SMA SB2500HF installation manual that its "startup voltage (adjustable)" was 220V but the "minimum voltage" was 175V.

His question was why not make the startup voltage as low as possible so the inverter kicks in earlier..

I promised I'd get back to him on it; any help much appreciated!
 
riight - you mean that it would therefore be wasting electricity? Wouldn't it be inverting the lower voltage DC power when it's on so be generating for longer?
 
Low input voltage doesnt mean it start up earlier - panels are at there highest voltage on a cold bright morning - and lowest voltage on a hot bright evening, so its wrong to assume inverters with a low voltage start sooner, its the opposite. I dont know the reason why they set the voltage at 220 and not 175, i can only assume the inverter is more effcient at 220 - its the same as saying this car can do 150 MPH, but crusing speed is 100MPH, everything has its sweet spot.

I welcome to be corrected if im mis-understanding.

Remember the cooler and brighter the day, the higher the voltage, the hotter it is the lower the voltage. Low volt inverters will stay on longer in the hottest weather, and high input means it will start on the coldest mornings.
 
Last edited:
Aye, & I understand the inverter's MPP tracker is 'moved around' by fluctuating the voltage it's working at - so that tallys with the efficiency being affected if you lower the starting voltage. Maybe lowering it effectively moves the bandwidth of the MPP tracker to the lower areas.

I'm with you that Voltage is affected by temperature whilst current is affected by insloation - have you ever Voc'd a panel that is totally covered over - must do that on my next install!
 
Folks

If I may add to the discussion;

Fundamentally the inverter will need enough power in the string(s) to stay connected to the grid. Without enough string(s) power, the reliability of inverter could be reduced (ie the grid connecting internal contactors could toggle on and off, hence reducing the lifetime of these components)


Therefore reduction of the activation voltage is not "a one size fits all" approach and needs to be applied in accordance with the output of manufacturers design software!
 
Hi BiggsSolar

I meant to add some dimension of time to my point! Assuming the inverter is connected to the grid and dosnt have the input power to inject current, it will wait for a given time before disconnecting (ie 60 secs as standard for Aurora, although adjustable). Given changing light conditions this could occur several times in a relatively small period.

Hope this helps

Regards all
 

Reply to Minimum start voltage & operating voltage in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

M
Evening all, I got called out to a job the other day were the customer has 2 x SB 1700's in the loft. The complaint was that the inverters cut out...
Replies
10
Views
3K
V
Hi Guys, i wish to change the start voltage on SB1700 inverter, manual says it is adjustable, any advise on how i can get this done. Cheers V
Replies
7
Views
6K
B
We recently installed a 10kW system on a rural farm building. The pre-existing incoming voltage was 257V ..... a single phase supply fed from a...
Replies
14
Views
3K
Blueflash
B
L
How does one determine the optimum start up voltage? I have a 3.6 kwp system in two equal strings into an Aurora 3.6 OUT inverter. Facing SSE with...
Replies
6
Views
3K
B
Hi, Firstly hello! and secondly I hope this is the right sub-forum. I read the annoucement and this seemed the most suited. I hope you don't...
Replies
10
Views
17K
BennyC
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock