because, according to it's psychiatrist, it needed to change.Why have you replaced the circuit breaker.
The company is ran by curious people.as i said. a MWC completed for the altered circuit. why a RA? is your company run by snowflakes?
Someone just informed me that "like for like" is a part p term.As far as I am aware, the requirement for a Risk Assessment when omitting RCD protection, is in relation to socket-outlets intended to be used for specific items of equipment.
The term ‘like for like’ is not used within BS7671.
ThanksA risk assessment is for departures from BS7671, see Regulations 120.3, 133.1.3 and 133.5 for such instances where this may be applicable. The risk assessment must prove that any departures do not affect the safety of the installation and persons using the installation and only apply to alterations and extensions to the circuit.
That is not correct. If you refer to the model Minor Works Certificate in BS7671 it clearly refers to the Regulations I have noted in #17 and this can cover a multitude of departures.Regulation 411.3.3 is the only instance where there is a requirement for a documented Risk Assessment in BS7671.
There are other Regulations where a Risk Assessment is required, but there is no requirement for the Risk Assessment to be documented in those instances.
I’m afraid it is correct.That is not correct. If you refer to the model Minor Works Certificate in BS7671 it clearly refers to the Regulations I have noted in #17 and this can cover a multitude of departures.
I'm so glad you guys are going to argue amongst yourselves so I can relax with my coffee.I’m afraid it is correct.
None of the Regulations you quoted require a documented Risk Assessment.
Finding out how to spell risk assessment, sorry Buzz honestthreasd going round in circles. where's buzz when youneed him?
I see no reason not to do that and lots of reasons to do so. If you read the notes in appendix 6 for person producing the certificate it's pretty clear you could but they use the term "may".Am i the only one who minor works everything?
If i change a cracked lightswitch like for like i carry out a full range of tests and certify it.
Reasons are habit, and also do alot of work in social housing so always wanting to cover my back. Photo of every job also saved in the computer job file.
Fair enough you can do that.An alteration would be if you changed something from the original design.
For instance, installing down lights in a room instead of a pendant.
An addition would be if you were to add something to the original design.
For instance, installing down lights in a room whilst leaving the pendant in place.
Replacing existing equipment because of damage or deterioration, would be maintenance.
Fair enough you can do that.
This article sums up my opinion better than I could..
Majoring in the Minor Works Certificate - https://professional-electrician.com/technical/majoring-minor-works-certificate-napit/
R1+R2 is taken at every point for eic.I have a little confusion over MWC's.
Currently we are adding a lot of smoke detectors to rental properties due to the change in the law around HMO licenses. Often its just upgrading from a D LD1 to a D LD2 system type. On smaller properties its just taking permanent feed off a local lighting fixture and putting a smoke detector in the living area, which is usually being used as a bedroom. And then wiring to smoke detectors in all the bedrooms upstairs from the exsisting one on landing via loft.
When completing MWC's for this above work its is necessary to perform R1+R2 for every fixture on the lighting circuit? A lot of these places have 1 lighting circuit feeding both floors so performing R1+R2 at every point takes a while and all I'm doing is adding 1 smoke detector. Would it be acceptable to confirm R1+R2 at my new smoke detector and the fixture immediately after, as I have not done anything that will affect the circuit beyond this.
Edit: A word
Zs technically doesn't prove cpc continuity though it is a good indication.IMO, you would not need to perform R1+R2 testing. a Zs reading would confirm cpc integrity and that reading can be entered on your MWC.
I've heard that grade of alarm is supposed to be interconnected. Is that true? If so how are you doing it?
It would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?Going back to the op original question , here is an example i come acroos a lot , carry out an eicr and there is a 32 amp mcb protection a 2.5mm radial socket circuit on the 2nd floor of an office.
We are then ask to carry out remedial work, now do you .
A. downrate to a 20amp mcb.
B. downrate to a 20 amp rcbo.
It would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?
B.Going back to the op original question , here is an example i come acroos a lot , carry out an eicr and there is a 32 amp mcb protection a 2.5mm radial socket circuit on the 2nd floor of an office.
We are then ask to carry out remedial work, now do you .
A. downrate to a 20amp mcb.
B. downrate to a 20 amp rcbo.
You Can't use lables on sockets now to say for specific use , they stoped that with the 18thIt would be odd not to use a rcbo unless you can jiggle something around upstream. No rcd = ra plus labels on sockets for specific use only. No?
Just curious... Does your alarm system signal something if one of the devices drops of the network? If so do mind telling what brand/range you're using?It differs from house to house but we generally install radio link bases downstairs from existing light fixtures then replace the existing landing smoke with a radio link and hard wire from there to upstairs rooms via the loft.
Don't usually know where last point on circuit is, usually not too hard to figure it out though.
Am i the only one who minor works everything?
If i change a cracked lightswitch like for like i carry out a full range of tests and certify it.
Reasons are habit, and also do alot of work in social housing so always wanting to cover my back. Photo of every job also saved in the computer job file.
No hope of me issuing a MWC to change a cracked light switch. I doubt house owners issue themselves a MWC when they replace a light switch.
Do you also issue a MWC when you replace a customer's light bulb?
I can see why you're not bothered but in a commercial installation where there might be a high turn over of staff, insane members of the public around etc would you not want to know if a socket has been changed once every 2 years for the last 6 years? That sort of info is very handy and MWC is best way to record itNo hope of me issuing a MWC to change a cracked light switch. I doubt house owners issue themselves a MWC when they replace a light switch.
Do you also issue a MWC when you replace a customer's light bulb?
It's your choice. He was only giving his opinion.
You Can't use lables on sockets now to say for specific use , they stoped that with the 18th
Just curious... Does your alarm system signal something if one of the devices drops of the network? If so do mind telling what brand/range you're using?