Discuss Minor Works in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
16
Hi

Quick question on a Minor works Cert Part 2. 3 Protective device on mod circuit do you eneter the device at the consunmer unit or if an appliacnce is feed via a fused spur do you enter the fuse?

please let me know

many thanks
steve
 
Device at cu as you are testing complete circuit.
 
Hi

Quick question on a Minor works Cert Part 2. 3 Protective device on mod circuit do you eneter the device at the consunmer unit or if an appliacnce is feed via a fused spur do you enter the fuse?

please let me know

many thanks
steve

sorry dont agree with sintra or acat, it has to be the fuse in the fsu for the addition as this the protection for the load side cable not the one at the ccu.

for example if you were to spur from an rfc with a 32A device at origin you could not deem it to protect a 1.5mm cable on the load side of the spur
 
I would agree with Trebor -

If you add a socket to a RFC then the 'Protective device for the modified circuit' is the 32A breaker in the CU.

But...

If your minor work is on a fused spur - say fitting new wall lights that are spured off a ring final - with a 5A BS1362 - then the 'Protective device for the modified circuit' is the 5A fuse.

Don't forget - in this scenario -, when measuring your Zs, your max Zs for your wall lights is the value given for a 5A BS1362, not the value for the 32A MCB protecting the ring final - because, as Trebor says, it could be wired in 1.5mm:)
 
I always enter the device at the CU as this is the device protecting the circuit you have modified and you are testing the entire circuit.....but in the comments section I will note that the section of the circuit that I have added/modified is protected by a bs1362 fuse and if neccessary record the max zs for that fuse as well.
 
Hi Everyone

Thanks very much for answering my question, the acctual job I'm reffering to was an immersion heater change. Therefore I did not modify the circuit as such the original immersion heater was fitted with a 13 a 3 pin plug!! which I changed to a fused spur.

Many Thanks

Steve
 
the socket you changed IS part of the original circuir and you CHANGED it to a fcu hence Minor works for the circuit as the circuit has been altered
 

Reply to Minor Works in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
875
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
919
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
637
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock