baggy61

Evening Gents,
I've just put some downlighters in a bathroom,as a replacement for a single fitting,fitted a 6A RCBO, & tested. Ze 35 ohms on a tt system but the existing board was 16th ed type fitted when the house was extended about 7 years ago.Fault current is'nt going to be high enough to operate cpds on non rcd protected circuits. The house is about 15 years old so presumably had RCD on meter tails when first built. What should I put on mwc?
 
I don't think you would have to mention it pal you are only responsible for the circuit that you are working on so only that has to be up to regs and you have fitted a rcbo which is you RCD protection so all good as far as I can see just do the MWC as normal
 
just include details of the circuit you have altered, along with Ze for the installation. i assume that you have checked earthing and bonding. you only need to certify your work. the rest of the installation is not your problem. however, if you see any issues you could make a note on the cert.
 
Hi baggy. Not sure if I read your post correctly. Are you saying it's a TT system without rcd protection for some circuits ?
If so, I would have wanted to rectify this before proceeding with any more works. Can't see a problem with the works you have done.
 
Hi baggy. Not sure if I read your post correctly. Are you saying it's a TT system without rcd protection for some circuits ?
If so, I would have wanted to rectify this before proceeding with any more works. Can't see a problem with the works you have done.

Sorry, didn't really answer your question. Just fill MWC as normal but make a note on it of your findings and make customer aware. May generate a little more work ?
 

Reply to Missing RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
8.5K shower unit is wired to plastic box consumer unit to 30 amp cartridge fuse with no RCD It’s the original shower installed when the house was...
Replies
19
Views
4K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock