Discuss MK consumer unit SPD's in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi all,
I'll be wiring up two small new builds, the customer is supplying all the materials, they supplied MK consumer units, the problem is it doesn't seem MK are doing SPD's for their boards.
Any one know of a SPD that fits MK boards?

Thank you in advance
 
Hi all,
I'll be wiring up two small new builds, the customer is supplying all the materials, they supplied MK consumer units, the problem is it doesn't seem MK are doing SPD's for their boards.
Any one know of a SPD that fits MK boards?

Thank you in advance
Do you actually need SPDs on your installs?
 
You don't have to fit them just because they are the new buzzword.
Read the regs and risk assessment. Speak to MK regarding their board.
 
Have a look at Reg 443.4 as there is an exception from fitting SPDs and from doing the risk assessment (that will always come out on the side of fitting them) for single dwelling units (flats, houses etc.) where the total value of the installation and equipment therein does not justify such protection.
 
Just out of interest, how many of you know of an instance where lightning has caused transient voltage to damage equipment in an installation?

Difficult to prove, but does happen. Happens more in countries which have a higher rate of electrical storms.
 
There's a website that shows where lightning is currently occurring. It's quite interesting.
 
unless you live in the middle of India and experience large amount of voltage surges then it isn't necessary to install spd's. especially for domestic property. if you do need one then put it in a seperate box near the cu and install a wylex one
 
Agree with Richey3333, SPD’s very handy not just about Lightning strikes worth installing nearly every time. Just wait till Arc protection becomes mandatory on all circuits other countries already doing it. Makes up for the cheap electrical items people like to purchase and the dodgy installations.
 
Agree with Richey3333, SPD’s very handy not just about Lightning strikes worth installing nearly every time. Just wait till Arc protection becomes mandatory on all circuits other countries already doing it. Makes up for the cheap electrical items people like to purchase and the dodgy installations.
I guess Arc protection will go the way of RCDs and become an integral part of the MCB?
 
Hi all,
I'll be wiring up two small new builds, the customer is supplying all the materials, they supplied MK consumer units, the problem is it doesn't seem MK are doing SPD's for their boards.
Any one know of a SPD that fits MK boards?

Thank you in advance


Try the Phoenix Contact 2804429. It’s a type II two pole Approved by MK for use in their CU’s.
 

Reply to MK consumer unit SPD's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
236
Hi everyone, Got a job converting commercial property into 4 flats, 2 up 2 down all with electric meters on the outside on ground floor, SWA to...
Replies
0
Views
627
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock