In this case you have a long final circuit, so you are going to see significant VD on that segment. As Lucian has said you generally want to spread the VD around (sorry if that phrase has unfortunate medical connotations...) so you don't have the sub-main or the final as being close to 5% and the other unrealistically heavy cable to keep down the rest.

You have a bit of fact-finding to do, but I suspect you are going to be better with a larger sub-main (such as 50mm 4C and parallel 25mm earth) so you have a bit more leeway at the Barn A for any extensions out (maybe even future feed to another building, etc) without needing to depend on decent 3P balance.

Get the facts together first!
Hooray, I have a basic grasp of VD. Now.... on to harmonics :-(

I'm joking please don't go on to harmonics, baby steps required.

Could I ask why you are suggesting a separate earth? Is it purely for cost, as it would be cheaper than a 5 core? Also, would my new thread make a difference to this? The new thread is talking about TT'ing the installation and whether it is necessary. If it was TT'd then could I just run a 4 core SWA as you suggest and no earth? The armour would be earthed (PME) giving the cable fault protection, and then it would be a TT at the barn.

Ps.. The customer is a nice chap but near impossible to get any facts from. @plugsandsparks post was highly insightful and accurate with regards this client!
 
Hooray, I have a basic grasp of VD. Now.... on to harmonics :-(

I'm joking please don't go on to harmonics, baby steps required.

:)

Could I ask why you are suggesting a separate earth? Is it purely for cost, as it would be cheaper than a 5 core? Also, would my new thread make a difference to this? The new thread is talking about TT'ing the installation and whether it is necessary. If it was TT'd then could I just run a 4 core SWA as you suggest and no earth? The armour would be earthed (PME) giving the cable fault protection, and then it would be a TT at the barn.
The reason is cost, it only needs to allow fault disconnection and possibly extraneous bonding if TN-C-S (another thread...)

4C cable is easier to find than 5C and cost is dominated by the amount of copper, so you might want to save it that way.

Now having said all of the above, 4C 50mm has 90mm^2 of steel armour so it meets the 10mm Cu equivalent for bonding if you have to. Next issue is the sub-main protection as your values for 4C SWA only are:
  • R1 = 0.387 mV/A/m
  • R2 = 1.8 mV/A/m
So if you know the Ze (which should be measured, but for TN-C-S ought to be below 0.35 ohms) and your length then you can compute the end of sub-main Zs and see if it allows disconnection on the supply fuse-switch in under 5s. A quick check in the OSG should answer that.
 

Reply to More on the 3 phase question..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
985
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
4K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top