Customer wants me to mount his EV charger on the back of an external, plastic meter cabinet. The cabinet is a new plastic one at the other side of his drive from the house with a separate consumer unit inside. This would be an ideal location for ease of installation.

Is this allowed or will I have to mount the charger on a separate post?

Can't find the regulation on this one. I have a sneaking suspicion it might be frowned upon by the DNO??


Screenshot 2023-07-08 at 05.45.54.png
 
Last edited:
Any internal view? What’s all inside?
Looks fairly easy to knock over. A steel bollard at each corner to protect?

Meter cabinets might have a sticker inside telling you not to use it for anything else.

The problem here is, if you drill the back to feed an EVCP, and water gets in, the DNO will blame you if their equipment gets damp and they need to attend.
 

Reply to Mounting EV charger on external meter cabinet in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock