Discuss MR11 3.5mm Spots stopped working in the Lighting Forum area at ElectriciansForums.net

SLOPPY

DIY
Reaction score
10
Hi all. I'm new to this forum so thank you for having me.

I'm having an issue with my bathroom lights. I have x4 MR11 3.5mm Spots. They've been up about 8 years without ever having to change a bulb. They are operated from a 2 switch cover outside the bathroom, one for the lights and the other switch for the fan, the fan is working fine.

Not sure if this is a coincidence, I have a razor socket inside the bathroom which I used for the very first time a few days back having received an electric toothbrush. Since using it, my lights stopped working.

I have replaced all the bulbs with new LED MR11 bulbs and unfortunately they still don't work.

Ive also removed the light switch cover and razor cover the check for loose wires, everything seems fine.

My expertise is wiring a plug only hence I've arrived here.


I would appreciate any advice before I call out an electrician.

Many thanks in advance.
 
Hi all. I'm new to this forum so thank you for having me.

I'm having an issue with my bathroom lights. I have x4 MR11 3.5mm Spots. They've been up about 8 years without ever having to change a bulb. They are operated from a 2 switch cover outside the bathroom, one for the lights and the other switch for the fan, the fan is working fine.

Not sure if this is a coincidence, I have a razor socket inside the bathroom which I used for the very first time a few days back having received an electric toothbrush. Since using it, my lights stopped working.

I have replaced all the bulbs with new LED MR11 bulbs and unfortunately they still don't work.

Ive also removed the light switch cover and razor cover the check for loose wires, everything seems fine.

My expertise is wiring a plug only hence I've arrived here.


I would appreciate any advice before I call out an electrician.

Many thanks in advance.
Is the shaver socket still working ?
Are all the other lights working ?
Is anything tripped in the consumer unit ?
 
Is the shaver socket still working ?
Are all the other lights working ?
Is anything tripped in the consumer unit ?
All 4 lights are not working in the bathroom, however all the upstairs lights are working fine.
The shaver socket is still charging my toothbrush.
Nothing is tripped on the consumer unit.
Thanks for your reply much appreciated.
 
All 4 lights are not working in the bathroom, however all the upstairs lights are working fine.
The shaver socket is still charging my toothbrush.
Nothing is tripped on the consumer unit.
Thanks for your reply much appreciated.
You really need to have a meter to check supplies.
It could be anything from a failed switch or a bad joint.
It's highly unlikely to be 4 failed transformers /lamps.
 
You really need to have a meter to check supplies.
It could be anything from a failed switch or a bad joint.
It's highly unlikely to be 4 failed transformers /lamps.
I have an electrical pen the lights up when you touch inside a socket.
Would you recommend I unsrew the double light switch and touch the connected wires individualy with the pen while the swith is in the on position.
Forgive me, I'm sure there must be an official name for the tester pen.

Update - it says its non contact voltage detector. It seems to work without unscrewing the switch fitting. I turn the pen on and it flashes red on both when I touch the switches.
 
Last edited:
I have an electrical pen the lights up when you touch inside a socket.
Would you recommend I unsrew the double light switch and touch the connected wires individualy with the pen while the swith is in the on position.
Forgive me, I'm sure there must be an official name for the tester pen.

Update - it says its non contact voltage detector. It seems to work without unscrewing the switch fitting. I turn the pen on and it flashes red on both when I touch the switches.
A non contact pen isn't a very reliable way of testing, It could be that you have a loss of the neutral.
 
You need to find out if the transformer has packed up.
 

Reply to MR11 3.5mm Spots stopped working in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
My bedroom light stopped working. The ceiling rose looks fine. No other lights are affected in the property and the fuses have not tripped. The...
Replies
18
Views
1K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
975
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
732
  • Locked
I've wired up my spots however the main light [the one that was once a ceiling rose] works as intended with the light switch, but the rest are...
Replies
2
Views
599

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock