Evening all,

Could some bright spark clarify something for me please.

In the OSG Table I1 Pg182 (Green) the values of resistance/metre or (R1+R2)/metre for copper and aluminium conductors assumes a value of 20 degrees as the ambient temperature.
Lets say a properties ambient temperature is 25 degrees I need to add in a multiplying factor from Table I2 Pg183. (I get this bit)

My question is, Is it assumed that the original temperature of 20 degrees stays as is, and you add an additional 5 degrees [correction factor 0.94] or,
add the multiplier for the expected 25 degrees [correction factor 1.02]

Your help as ever is appreciated
 
Thanks for your reply. I'm aware you mutiply it. My question was particular to the correct choice of correction factor. So in Table I1 there is the asumption that ambient temperature of 20 degrees. If the ambient temperature is in fact 25 degrees do I a) add a 5 degree correction factor in effect making it up to 25 degrees or b) use the 25 degree correction factor.

Thank you in advance
 

Reply to Multiplers - ambient temperatures in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
923
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
8K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock