The 16A MCB is wrong . It is 6 A, sorry. 2 Main switches because I want Shed and outdoor lighting be separate)Why 2 main switches?
You don't get 63mA and 80mA RCDs. I think you are confused with the maximum operating current.
Outside lighting on a 16A MCB - maybe a bit OTT?
I would go for a full RCBO unit with an SPD.
I have made another mistake in writing. These are 80A,63 A and 40A RCDsThe 16A MCB is wrong . It is 6 A, sorry. 2 Main switches because I want Shed and outdoor lighting be separate).
Yes, RCBOs are better, I will have more space as well.I think you'd be better off with a single 100a main switch then use individual RCBOs for all circuits. This would provide better discrimination in the event of an earth fault on any final circuit.
Yes, RCBOs are better, I will have more space as well.
I have uploaded the revised image. I will have a small consumer unit in the shed being fed from here. I am not sure if it is wise to feed the shed CU from a a RCBO in this main CU!?Why 2 main switches?
You don't get 63mA and 80mA RCDs. I think you are confused with the maximum operating current.
Outside lighting on a 16A MCB - maybe a bit OTT?
I would go for a full RCBO unit with an SPD.