OK we have progress, but more questions.
So please humour the newbie =)
The dc measurement is more accurate so I pinned the end of the other ring to the Pc socket.
I disconnected the wires at the back of the relevant sockets. Long lead the n to confirm the link. Then r1r2 the other legs to check they were fine.
Sorted, b16 is in! I'll get the b20 if I nuisance trip. (can you guess which county I live in).
So eicr question.
What would you code the discolouration of the (original) mcb. I'd go c3 as the problem is identified and repaired.
I've also run the calcs on the single spur originally for cpc.
Now the earth fault current is 800a, which is too much for a 1.5mm mcb. However as there is rcd protection am I allowed to use the 40ms or actual trip time to calculate cable overheat?
However a l-n short will give a 1.2kA fault current. The circuit will trip in 0.1s
Unless I've got the formula wrong (or totally misunderstood) minimum CSA needs to be over 3.2....
S>{root(i²t)} /k
Have I got this wrong?
Thanks
So please humour the newbie =)
The dc measurement is more accurate so I pinned the end of the other ring to the Pc socket.
I disconnected the wires at the back of the relevant sockets. Long lead the n to confirm the link. Then r1r2 the other legs to check they were fine.
Sorted, b16 is in! I'll get the b20 if I nuisance trip. (can you guess which county I live in).
So eicr question.
What would you code the discolouration of the (original) mcb. I'd go c3 as the problem is identified and repaired.
I've also run the calcs on the single spur originally for cpc.
Now the earth fault current is 800a, which is too much for a 1.5mm mcb. However as there is rcd protection am I allowed to use the 40ms or actual trip time to calculate cable overheat?
However a l-n short will give a 1.2kA fault current. The circuit will trip in 0.1s
Unless I've got the formula wrong (or totally misunderstood) minimum CSA needs to be over 3.2....
S>{root(i²t)} /k
Have I got this wrong?
Thanks