Search the forum,

Discuss Thoughts on recent EICR welcomed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

What's the risk if live conductors are connected together?
On a normal circuit, negligible to none (assuming you have correctly linked them) if wiring has been correctly installed and with all appliances up to relevant standards.

But in most cases some checks have been done on the circuit first, so you are confident that the wiring is correctly identified at the CU end. Or you at least know what the circuit is and can verify that nothing unusual is installed on it.

When it's an unknown circuit I'd be much more wary - he may have done a 250V one first of course, which wouldn't be noted... Or the figures may have been all plucked from thin air...

For an unknown circuit, a L-N test would actually be useful (even if at 250V) - as it would give future inspectors some clue as whether there was a current load on the circuit, or if it was likely an obsolete item that had been terminated...

I know that the risk is probably minimal regardless, but I still wouldn't want to find out that some expensive aquarium or medical equipment suddenly stopped working just after I'd zapped it without taking due care...
 
1.I agree it’s not assentail I just think if theirs a box for it on the form it’s a bit lazy to leave it blank. Especially as it’s not a particularly big house or that cluttered with furnitures
2. I agree I don’t normally records r1&r2 reading on a EICR. Was the fact he put readings down for some some circuits but left others blank. I think you should either fill them all out or put LIM for them all
4.he might mean open circuit, but it should be blank since it’s a radial and I’m the board u can see two cables, one going through the back and another coming out the top of the board and into a socket next to the board
5.no the cables go straight into the tncs earth block with 6mm and 10mm for bonding coming out of it
8.loads not very high about 6 pendants, bathroom light, 1 or 2 lights in the kitchen and door bell transformer
10.sockets can be plugged into to confirm polarity and earthing, cooker theirs a junction box behind the oven to confirm polarity and earthing. He has zs and r1&r2 readings for cooker, zs reading for sockets and both had polarity box ticked.
which is why I would say it should c3 or lim instead of FI.
also I noticed their was a hole in the side of the cooker switch which he must of done trying to get it if the wall
12.I agree with what you said but he put c2 lack of rcds on sockets, c2 rcds in bathroom ,c3 for cables hidden in wall then c3 for overall additional rcd protection at db which I thought should be c2.
He also put c2 for rcd offering fault protection which is either wrong cause it’s tncs or because of the high zs on the sockets but then it should be noted in the codes
14.what he’s saying is the oven should be fused down to 13 amp not feed directly from the cooker circuit but it doesn’t come with pre fixed flex, is feed with 6mm cable and on top of the oven it clearly states total wattage 4990.
If that was the only fault then the installation would be failed just because of that which I think is wrong
Appears that having an > symbol included on many of the readings would have made things a bit clearer. Are they the over printed certificate type?

Not sure if 7671 says anything about blank boxes actually, though I guess they suggest no reading was taken - personally I do fill in N/A, LIM or -- on most of them just because it looks better imo.

I guess the socket circuit would be a C2 either for being radials on 30A fuse, or a RFC with no continuity - that one might well be a fair FI if it wasn't clear, though also a safe C2.

Were there single insulated cables at the cooker point? - If it was possible to test polarity and earthing from the front of the points, then I'd agree that FI seems unjustified.

The RCD for fault protection box, along with the alternative supply arrangement boxes is one of the first places to look to see if someone knows what they are actually filling out.

The pendants is another interesting one - use of unsheathed flex is down as a C3 in BPG4, whereas I've always replaced them when I've seen them before and would probably veer towards C2. Not sure what the rational behind that is where unsheathed flex would be a C2 anywhere else... (perhaps they think it's considered not accessible to touch)

Still end up with 4 or so C2s I guess, and noone ever looks past the first page anyway.

Out of Interest, was this a fully registered Approved Contractor or equivalent? The quality of reports I've seen from people who are in theory at a higher level than me has been a disappointment over the last year or so - makes me feel better about the quality of the ones I issue though at least (some of which will no doubt have mistakes in).

Not sure what the solution is, only a strong belief that the 'powers that be' aren't competent enough to find it!
 
Yes was a couple of cable behind the oven which need cleaning up,
There a junction box behind the oven to check the polarity and earthing so I thought F1 was abit over the top. A C3 would of been more appropriate for the inaccessible cooker switch
The test sheet he used was the nic approved contractor ones so I assume so
 

Reply to Thoughts on recent EICR welcomed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
679
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
605
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
784
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
899

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top