I have a separate fan and light dimmer I was replacing to a different color. I took pictures before I unhooked on my fiancés phone. Unhooked everything and those pictures are no longer on her phone. I was able to trace all the wires but two need some help hooking everything up.

There are four sets of wires coming in the box.

Left - black and white. Not sure where these go but I think it's an outlet behind my dresser.

Second - black and white. Black is power from breaker box. The same black wire comes out of the ceiling which looks to be wrapped in electrical tape. . White goes to outlet in same room.

Third - black white and red - All three go to the outlet mentioned above.

Fourth - black and white and ground. Black goes to black wire coming out of ceiling. White comes out of the ceiling as does ground.

Ceiling has two black wires, one white and one ground.

There was also a jumper wire.

Currently I have the black wire from the breaker connected to a jumper going to thevred wire. So that outlet will work as I have my tv plugged into it.

Red Dots wires on the left
Green dots are wires coming out of second row
Blue dots third row
Yellow dots fourth
White dot is hot wire
 

Attachments

  • PXL_20201028_003904375~2.jpg
    142.1 KB · Views: 14
From a distance now you have lost the pics, impossible to predict which wire goes where.
 
From a distance now you have lost the pics, impossible to predict which wire goes where.
I traced them out and put it in the main post. Posted the picture with color code to tell you where each wire goes.

In the post

First, second, third, fourth are descriptions of the wire and where I traced them too.

I color coded in the picture for reference.
 

Attachments

  • PXL_20201028_003904375~2.jpg
    142.1 KB · Views: 6
  • PXL_20201028_003937185.jpg
    156.2 KB · Views: 5
Last edited:
Some of that makes sense but at the moment there are too many variables.

You have the right number of wires in the celiing: two black hots, one for fan, other for light, a white neutral and a ground. At the wall you have what seems to be an incoming feed from the panel via an outlet (you say the neutral goes via the outlet, I would infer the hot does too) and an onward feed to the outlet powering the TV.

One would expect the neutral in, out and to the ceiling all to be connected together; the hot in and out to be connected and also pigtailed to the two switches / dimmers, and then the two controlled hots out of those to head up to the fan and light.

But I can't make sense of:
The same black wire comes out of the ceiling
when referring to the feed from the panel / previous outlet.
And it's not clear why the next outlet beyond the switch has a red and a black hot... was one half of a duplex controlled by the switch and the other not? And there don't seem to be two black hots leaving the switch box towards the ceiling.

So it needs further investigation / clarification. You might need to access the outlet behind the dresser, and double-check the situation with the incoming power feed to make sure the hot and neutral are correctly identified, coming from the same place in the same run of cable. An electrician would probably make a quicker job of it with less chance of error, simply through experience.
 
Last edited:
I have a separate fan and light dimmer I was replacing to a different color. I took pictures before I unhooked on my fiancés phone. Unhooked everything and those pictures are no longer on her phone. I was able to trace all the wires but two need some help hooking everything up.

There are four sets of wires coming in the box.

Left - black and white. Not sure where these go but I think it's an outlet behind my dresser.

Second - black and white. Black is power from breaker box. The same black wire comes out of the ceiling which looks to be wrapped in electrical tape. . White goes to outlet in same room.

Third - black white and red - All three go to the outlet mentioned above.

Fourth - black and white and ground. Black goes to black wire coming out of ceiling. White comes out of the ceiling as does ground.

Ceiling has two black wires, one white and one ground.

There was also a jumper wire.

Currently I have the black wire from the breaker connected to a jumper going to thevred wire. So that outlet will work as I have my tv plugged into it.

Red Dots wires on the left
Green dots are wires coming out of second row
Blue dots third row
Yellow dots fourth
White dot is hot wire

Some of that makes sense but at the moment there are too many variables.

You have the right number of wires in the celiing: two black hots, one for fan, other for light, a white neutral and a ground. At the wall you have what seems to be an incoming feed from the panel via an outlet (you say the neutral goes via the outlet, I would infer the hot does too) and an onward feed to the outlet powering the TV.

One would expect the neutral in, out and to the ceiling all to be connected together; the hot in and out to be connected and also pigtailed to the two switches / dimmers, and then the two controlled hots out of those to head up to the fan and light.

But I can't make sense of:

when referring to the feed from the panel / previous outlet.
And it's not clear why the next outlet beyond the switch has a red and a black hot... was one half of a duplex controlled by the switch and the other not?

So it needs further investigation / clarification. You might need to access the outlet behind the dresser, and double-check the situation with the incoming power feed to make sure the hot and neutral are correctly identified, coming from the same place in the same run of cable.
The outlet where the tv plugs into has two white wires, two black wires and two reds. I'll have to check the other outlet. I really appreciate the feedback.
 

Reply to Need help rewiring two dimmers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
466
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
321
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
230
Trying to install a Lutron Toggle/Dimmer (TGCL-153PR) Confused, as the current switch has 3 wires gong to it Black, White, and Red (there is also...
Replies
1
Views
628
FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock