Hi all im looking for some guidance please.

i dont have much experience with heating systems but done plenty of domestic. This is my own house and here is what i have:

ideal logic 35 (logic not logic plus)
danfoss tp5000 stats x2
2 zone valves
nest 3rd gen kit

im aware a nest is needed for each zone and ill buy another but for the minute, the second zone runs one radiator only in one room. im going to consider doubling it up into one until i have money for the second nest in a few months.

right so its a new build with feed to boiler spur and 5 core into boiler. the boiler has mains voltage on the thermostat connections and i have installed my heatlink via a 5 core and done the mains power plus the opentherm connection. nest all operational at this point.

The danfoss 5000's have a 3 core to each from wiring centre and i understand most of the system wiring. 4 cores into valves. stats are wired as n/o contacts.

im having issues figuring how to go about removing the old stats and powering the nest when i wall mount it. its currently via usb.
the stats have mains switching for the valves as does the boiler on the stat connections.

please can anyone shed some light? i think the nest may not be operating correctly and calling for heat because of the existing stats. i know they need to go eventually but i just wanted to test at this point. i think the stats are holding it off calling for heat.

im i right in thinking remove the 3 cores from wiring centre to stats if not needed and connect valve switch wires to permenant feed to keep them open?
im just lost as to how to get low voltage at wall for nest and mains at valves

thanks for bearing with my waffle and i really appreciate any help
 
Why have you left the old heating controls connected? It sounds like a bit of a fudge now.
Hi I have no intention of leaving them connected in the long run. I have 2 stats and 2 valves.
I wanted to ensure the nest runs on the opentherm without issue and it doesn't with the current stats connected. I need to know what I need to do in order to disconnect them yet satisfy the nest. What I have done so far is simply add the heatLink power and opentherm connection. The stats are holding the the valves off but the nest is calling for heat via the opentherm. I'd like to remove the old stats once I know if there is anything I need to do with the valve connections given they are 4 core. Cheers
 
Why have you used the OpenTherm connections? Nest Diagrams have one for S Plan which you seem to have, follow it and you'll need to ditch the existing controls
 
Why have you used the OpenTherm connections? Nest Diagrams have one for S Plan which you seem to have, follow it and you'll need to ditch the existing controls
I'd been advised opentherm modulates both heating and hot water which of both can be seen and adjusted via the app
 
No. Prob best to get someone in.
Cheers for your help so far. You have helped more than the forum police.
I'm just going to leave this thread. I quoted at the start this was in my own home. In light of this thread, the police opened another completely separate thread to have a rant about folk wanting for nothing.
I'm a spark with 236, 17th update and my part p with 20 yrs in the trade yet I can't get a little hope from fellow sparks. I'm not asking to be spoon fed nor doing a job for a customer I'm not competent to do.

Maybe I'll pay another spark who has become nest pro (answered an online quiz) like all other sparks would.

Good evening to you all
 
I stopped trying to work out peoples heating systems when i was presented with a enclosure full of disconnected and incorrectly terminated wires with connector blocks, the customer had tried to install his own nest and didnt quite understand what he was doing. he started trying various combinations to try and get it all working before asking for help, so I looked at the mess and said no thanks. wires were all over place and according to the paperwork was Y plan. i wasnt going to spend ages working out which wire was which and putting it back together. He took hindrance at my call out fee doubling for being a saturday afternoon. Some jobs are more trouble than they are worth.
 
Cheers for your help so far. You have helped more than the forum police.
I'm just going to leave this thread. I quoted at the start this was in my own home. In light of this thread, the police opened another completely separate thread to have a rant about folk wanting for nothing.
I'm a spark with 236, 17th update and my part p with 20 yrs in the trade yet I can't get a little hope from fellow sparks. I'm not asking to be spoon fed nor doing a job for a customer I'm not competent to do.

Maybe I'll pay another spark who has become nest pro (answered an online quiz) like all other sparks would.

Good evening to you all
Cheers for your help so far. You have helped more than the forum police.
I'm just going to leave this thread. I quoted at the start this was in my own home. In light of this thread, the police opened another completely separate thread to have a rant about folk wanting for nothing.
I'm a spark with 236, 17th update and my part p with 20 yrs in the trade yet I can't get a little hope from fellow sparks. I'm not asking to be spoon fed nor doing a job for a customer I'm not competent to do.

Maybe I'll pay another spark who has become nest pro (answered an online quiz) like all other sparks would.

Good evening to you all
To be fair no one knows your an electrician as you haven't stated such on your profile and not in the opening post either.
 
To be fair no one knows your an electrician as you haven't stated such on your profile and not in the opening post either.
Cheers buddy. I didn't mean to go off on one. I appreciate all the folk come here expecting to be given free information. I opened a new profile thinking mine had been closed since I have not been active on the forums for about 3yrs. I didn't get a password reset. Yahoo is crap like that and takes ages. I put a brief note in my profile so people would see I'm not here to scrounge info and potentially harm myself or others. I'll add some more info. Here is my profile I set up this afternoon.

If anyone wishes to still help me then I'd be grateful.

Cheers

IMG_0005.PNG
 
Cheers buddy. I didn't mean to go off on one. I appreciate all the folk come here expecting to be given free information. I opened a new profile thinking mine had been closed since I have not been active on the forums for about 3yrs. I didn't get a password reset. Yahoo is crap like that and takes ages. I put a brief note in my profile so people would see I'm not here to scrounge info and potentially harm myself or others. I'll add some more info. Here is my profile I set up this afternoon.

If anyone wishes to still help me then I'd be grateful.

Cheers

View attachment 40355
I'm not 100% but I don't think you can have two nests set up as open therm.
 
I'm not 100% but I don't think you can have two nests set up as open therm.
I'll cross that bridge when it comes to it I think. To pass regs my house (a bungalow has been zoned into two. The second zone runs the lounge only. I know what people will say about me altering this but that's for another day. The nest is connected to opentherm and without altering the current stats and initial install at all, it appears the nest calls for heat, the boiler fires but the valves don't open due to n/o stat connections.
The stats are wired from the control centre supplying mains at both stats via 3 cores. I can't see how without either altering the wiring at the boiler spur or locating heat link at the wiring centre cupboard I'll achieve 12v at the wall stat. For now I'm happy with running nest via USB if I can confirm isolation of wall stats is ok. Obviously this means some connection altering. I do intend on buying a second nest and remove one stat now if poss as per nest say is possible
 
The brown of the two port needs connecting to heating on of the heatlink.
Cheers

So the opentherm is supposed to be able to control both heating and hot water via the one pair connection.
I have a 3 core from boiler spur to wiring centre and 3 core to each stat. Brown on each valve to sw return from each stat. I understand the wiring of what's in place.
I'm trying to figure out best way to achieve 12v at wall stats and not kill the feed to the valves. I think this leaves me with 2 options. Adjust wiring at spur or install heat link in wiring centre cupboard and use 2 legs from the 3 core back to boiler for opentherm. The 2 valves are for both zone use and not domestic hot water

Img
 

Reply to nest installation issues in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Hi guys, Do you know if I can install a Nest E with the heat link in the airing cupboard as opposed to the room stat position? System is a S plan...
Replies
1
Views
709
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
672
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock